There are times when you can't get an exact measure and you have to make
assumptions.  That's why you don't calc systems to within 1 psi between
demand and available.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Wednesday, February 13, 2008 11:24 AM
To: [email protected]
Subject: RE: C-Factor for old piping


Do you always test a Hydrant next to the Riser?  

If you do that, that is fine. 

Or you perform test some distance away and make assumptions that the
pipe connecting between the point of test and the riser including the
service connection, water meter, backflow, filter will all follow Mfg
data and H-W formula with C factor 120? 

Or you have an old main and you install a pump house some distance from
the risers and assume that the pipe will follow H-W formula with C
factor 120? .

These are all assumption. 


Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of ?... ....
Sent: Wednesday, February 13, 2008 4:34 PM
To: [email protected]
Subject: C-Factor for old piping

i may not be following your point,
but if you are concerned that the actual C-factor of old UG pipe is less
than the idealized C-factor

what does it matter
as long as you take your source where ever your gauge hydrant is?

the waterflow test will account for any aging in the pipes,
automatically.

it is another thing,
to extend this thinking,
downstream of the
guage hydrant though.
There you will need
professional judgement
to bring
value engineering.

scot deal
excelsior fire



On Feb 13, 2008 1:19 PM, danarbel <[EMAIL PROTECTED]> wrote:

>
>
> According to 22.4.4.7 Friction Loss, The C-Factor used for black steel

> pipe is 120.
>
> My question is:
>
> In case of using old pipe system Mains for water supply of sprinkler 
> system,
>
>
> Is there in the code any requirement to find out by actual testing 
> that the piping determined as adequate by the hydraulic calc procedure

> is indeed adequate?
>
> Thanks
>
>
> Dan Arbel
> Tel: 972-4-8243337
> Fax: 972-4-8243278
> M: 972-52-2810593
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.516 / Virus Database: 269.20.4/1275 - Release Date:
> 12/02/2008
> 15:20
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.4/1275 - Release Date:
12/02/2008 15:20
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.4/1275 - Release Date:
12/02/2008 15:20
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to