If you have a pressure reducing valve you don't have to have the check
valve.


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Thursday, February 14, 2008 10:24 AM
To: [email protected]
Subject: Re: Check valve on floor control assembly

8.17.5.2.2(1)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Ed Kramer" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, February 14, 2008 8:54 AM
Subject: RE: Check valve on floor control assembly


> Cliff, I'm not aware of anything in 13 that requires the check valve. 
> Also
> worth noting, nothing in 13 requires that each floor has its own control
> valve (except for high rises, I think).  I tried to find the section that
> requires the control valves in high rises but couldn't.  Anyone know if 
> it's
> been removed, or am I just missing it?
>
> Ed Kramer
> Littleton, CO
>
>> -----Original Message-----
>> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
>> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
>> Sent: Wednesday, February 13, 2008 1:50 PM
>> To: [email protected]
>> Subject: Check valve on floor control assembly
>>
>> NFPA 14 requires a check valve on a floor control assembly for a
>> connection
>> to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
>> Does
>> this requirement cross over to NFPA 13 for a riser in a multi-story
>> building
>> that is not actually a standpipe?  Like for a 3-story bldg that isn't
>> high
>> enough to require a standpipe.
>>
>>
>>
>> I understand that it would be a good idea for the same reasons it is
>> required on a standpipe but is it actually a requirement?
>>
>>
>>
>> Cliff Whitfield, SET
>>
>> Fire Design, Inc.
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to