If you have a pressure reducing valve you don't have to have the check valve.
Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Thursday, February 14, 2008 10:24 AM To: [email protected] Subject: Re: Check valve on floor control assembly 8.17.5.2.2(1) Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Ed Kramer" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Thursday, February 14, 2008 8:54 AM Subject: RE: Check valve on floor control assembly > Cliff, I'm not aware of anything in 13 that requires the check valve. > Also > worth noting, nothing in 13 requires that each floor has its own control > valve (except for high rises, I think). I tried to find the section that > requires the control valves in high rises but couldn't. Anyone know if > it's > been removed, or am I just missing it? > > Ed Kramer > Littleton, CO > >> -----Original Message----- >> From: [EMAIL PROTECTED] [mailto:sprinklerforum- >> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield >> Sent: Wednesday, February 13, 2008 1:50 PM >> To: [email protected] >> Subject: Check valve on floor control assembly >> >> NFPA 14 requires a check valve on a floor control assembly for a >> connection >> to a standpipe that is part of a combined system. (6.3.5.1 2007 ed) >> Does >> this requirement cross over to NFPA 13 for a riser in a multi-story >> building >> that is not actually a standpipe? Like for a 3-story bldg that isn't >> high >> enough to require a standpipe. >> >> >> >> I understand that it would be a good idea for the same reasons it is >> required on a standpipe but is it actually a requirement? >> >> >> >> Cliff Whitfield, SET >> >> Fire Design, Inc. >> >> >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email to:Sprinklerforum- >> [EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)