Dear colleagues,
A plant owner has a new sprinkler system. Installation started 2
years ago. Final acceptance was approx. 6 month ago. All sprinkler
piping is (interior and exterior) hot dip galvanized steel. Some
systems are dry, some are wet and some contain water + 1% AFFF-concentrate.
A few month ago a mechanial crew was welding some process piping and
accidentally cut a sprinkler pipe.
The mechanics claim that a flash flame came out of the sprinkler pipe!
This caused some disturbance as you can imagine.
An investigation is going on since.
Recently someone with a lab told our client that MIC bacteria may
have produced combustible gas that could have been collected in the
sprinkler pipe.
Question: is there any chance that this can be true?
Or should we look for another cause?
Frans Stoop
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)