If the system is a combination standpipe and sprinkler system NFPA 14 6.2.5
states "each connection to the sprinkler system shall have an individual
control valve and check valve of the same size as the connection". Si it is
usually not a big deal to provide and also makes it easier to test large
systems.
VTY,
Peter Nadhazy Cell (508)493-3933
Marathon Fire Protection, Inc.
578 Arcade Avenue
PO BOX 160
Seekonk, MA 02771
(508)336-4300
Fax :(508)336-4232
email: [EMAIL PROTECTED]
www.marathonfire.com
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, February 14, 2008 11:53 AM
Subject: Re: Check valve on floor control assembly
We ALL think that but 13 is a tad weak on addressing high rises except
for combined sprinkler standpipes (so in a back door manner catches
most). 13 addresses two items:
Where each sprinkler system on each floor is equipped with a separate
water flow device, it shall be connected to an alarm system etc etc.
Doesn't say you have to provide the thing.
It's also amusing that the floor control valve in Figure A.8.17.4.2 (b is
not discussed in that section of the body. Actually 8.16.1.1.2.2
mentions the floor control valve by saying that it will be supervised per
8.16.1.1.2.1. Doesn't say you have to have it. As already identified,
the building code takes care of that.
It is one of those things that most of us have always done and think it
must be cleanly addressed in 13 (until you actually look at). This is
just like the requirement for having a check valve in every riser. You
won't find that either.
LIke a few other things, since no one is submitting proposals on it, it
isn't on the radar screen of the TC.
Roland
On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote:
Cliff, I'm not aware of anything in 13 that requires the check valve.
Also
worth noting, nothing in 13 requires that each floor has its own control
valve (except for high rises, I think). I tried to find the section
that
requires the control valves in high rises but couldn't. Anyone know if
it's
been removed, or am I just missing it?
Ed Kramer
Littleton, CO
-----Original Message-----
From: [EMAIL PROTECTED] [mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of Cliff Whitfield
Sent: Wednesday, February 13, 2008 1:50 PM
To: [email protected]
Subject: Check valve on floor control assembly
NFPA 14 requires a check valve on a floor control assembly for a
connection
to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
Does
this requirement cross over to NFPA 13 for a riser in a multi-story
building
that is not actually a standpipe? Like for a 3-story bldg that isn't
high
enough to require a standpipe.
I understand that it would be a good idea for the same reasons it is
required on a standpipe but is it actually a requirement?
Cliff Whitfield, SET
Fire Design, Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)