I didn't see anyone speak to this earlier; check valves on floor controls hold 
in system pressure in case the riser (or standpipe) needs to be drained for 
some reason.  In a highrise, that could mean a lot of drain-down or having to 
close each floor control valve. 


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: Roland Huggins <[EMAIL PROTECTED]>

Date: Thu, 14 Feb 2008 08:53:37 
To:[email protected]
Subject: Re: Check valve on floor control assembly


We ALL think that but 13 is a tad weak on addressing high rises  
except for combined sprinkler standpipes (so in a back door manner  
catches most).   13 addresses two items:

Where each sprinkler system on each floor is equipped with a separate  
water flow device, it shall be connected to an alarm system etc etc.   
Doesn't say you have to provide the thing.

It's also amusing that the floor control valve in Figure A.8.17.4.2 
(b  is not discussed in that section of the body.  Actually  
8.16.1.1.2.2 mentions the floor control valve by saying that it will  
be supervised per 8.16.1.1.2.1.  Doesn't say you have to have it.  As  
already identified, the building code takes care of that.

It is one of those things that most of us have always done and think  
it must be cleanly addressed in 13 (until you actually look at).    
This is just like the requirement for having a check valve in every  
riser.  You won't find that either.

LIke a few other things, since no one is submitting  proposals on it,  
it isn't on the radar screen of the TC.

Roland

On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote:

> Cliff, I'm not aware of anything in 13 that requires the check  
> valve.  Also
> worth noting, nothing in 13 requires that each floor has its own  
> control
> valve (except for high rises, I think).  I tried to find the  
> section that
> requires the control valves in high rises but couldn't.  Anyone  
> know if it's
> been removed, or am I just missing it?
>
> Ed Kramer
> Littleton, CO
>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]  
>> [mailto:sprinklerforum-
>> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
>> Sent: Wednesday, February 13, 2008 1:50 PM
>> To: [email protected]
>> Subject: Check valve on floor control assembly
>>
>> NFPA 14 requires a check valve on a floor control assembly for a
>> connection
>> to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
>> Does
>> this requirement cross over to NFPA 13 for a riser in a multi-story
>> building
>> that is not actually a standpipe?  Like for a 3-story bldg that isn't
>> high
>> enough to require a standpipe.
>>
>>
>>
>> I understand that it would be a good idea for the same reasons it is
>> required on a standpipe but is it actually a requirement?
>>
>>
>>
>> Cliff Whitfield, SET
>>
>> Fire Design, Inc.
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to