We ALL think that but 13 is a tad weak on addressing high rises
except for combined sprinkler standpipes (so in a back door manner
catches most). 13 addresses two items:
Where each sprinkler system on each floor is equipped with a separate
water flow device, it shall be connected to an alarm system etc etc.
Doesn't say you have to provide the thing.
It's also amusing that the floor control valve in Figure A.8.17.4.2
(b is not discussed in that section of the body. Actually
8.16.1.1.2.2 mentions the floor control valve by saying that it will
be supervised per 8.16.1.1.2.1. Doesn't say you have to have it. As
already identified, the building code takes care of that.
It is one of those things that most of us have always done and think
it must be cleanly addressed in 13 (until you actually look at).
This is just like the requirement for having a check valve in every
riser. You won't find that either.
LIke a few other things, since no one is submitting proposals on it,
it isn't on the radar screen of the TC.
Roland
On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote:
Cliff, I'm not aware of anything in 13 that requires the check
valve. Also
worth noting, nothing in 13 requires that each floor has its own
control
valve (except for high rises, I think). I tried to find the
section that
requires the control valves in high rises but couldn't. Anyone
know if it's
been removed, or am I just missing it?
Ed Kramer
Littleton, CO
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of Cliff Whitfield
Sent: Wednesday, February 13, 2008 1:50 PM
To: [email protected]
Subject: Check valve on floor control assembly
NFPA 14 requires a check valve on a floor control assembly for a
connection
to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
Does
this requirement cross over to NFPA 13 for a riser in a multi-story
building
that is not actually a standpipe? Like for a 3-story bldg that isn't
high
enough to require a standpipe.
I understand that it would be a good idea for the same reasons it is
required on a standpipe but is it actually a requirement?
Cliff Whitfield, SET
Fire Design, Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)