I attended a meeting where sprinkler designers and contractors expressed 
concern regarding liability despite what the building code says and frankly one 
must appreciate their concern.

With that said there exists a low cost method, i.e. sheathing the underside, to 
achieve compliance all the way around and where a fire official can intervene 
with the architect.

And yes Mike agreed on Fire Officials making design decisions, but then again 
the blame lies with whomever opens that door in the first place.

John Drucker


 

 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown 
(TECH- GVL)
Sent: Friday, February 22, 2008 10:31 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

There are two issues with a sprinkler.  Those are sensitivity and distribution. 
 The sidewall sprinklers must be tested to insure that they provide the 
appropriate sensitivity and distribution in distribution tests (RDD & ADD) as 
well as sensitivity tests and fire tests.  I would not think that having a fire 
official just deciding one was better than the other is a really good idea.  
That smacks of the fire inspector saying he wants something done just because 
"he wants it that way".  

Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, February 22, 2008 9:20 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

There seems to be a consensus among the inspector's I know that the sidewall is 
better than a pendent in many cases because of the spray pattern. Would there 
be a significant difference in the time it takes to fuse the two different 
types of heads?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Friday, February 22, 2008 7:47 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

Check The International Building Code which requires sprinklers protecting some 
decks and in that section the IBC allows deviations from NFPA 13 or the 
sprinkler listing.  Maybe some bleed over into exterior canopies.

Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Thursday, February 21, 2008 5:44 PM
To: [email protected]
Subject: Dry HSW under open framed 2x's

I'm noticing a lot of small exterior canopies being protected with dry 
horizontal sidewall sprinklers even though it is open framing (usually 2X6's or 
2X10's at 24"
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed 
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question, 
they aren't smooth so how are people getting away with this? Smooth being 
defined as sructural members being spaced more than 7'-6" o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's okay 
for a pendant why not a HSW? (I'm sure it has to do with the intracacies of 
unfamiliar testing and listing requirements of a pendant over a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows:     
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where specifically 
listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small 
unheated areas can be protected by dry-pendent sprinklers extending through the 
wall from wet sprinkler piping in an adjacent heated area. Where protecting 
covered platforms, loading docks, and similar areas, a dry pendent sprinkler 
should extend down at a 45 degree angle. The width of the area to be protected 
should not exceed 7½ ft (2.3 m). Sprinklers should be spaced not over 12 ft 
(3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as used 
in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced 
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or 
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses spaced 
more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on metal 
lath or a combination of materials of equivalent fire-resistive rating attached 
to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids, 
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that specified 
under item (d) and attached to the underside of wood joists, wood trusses, and 
bar joists 

       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to