Right, but I can not count the sidewalls I have seen poking out under decks
in 13 applications.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Friday, February 22, 2008 11:59 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

Greg,
   
  It looks like the residential use of HSW for open framed patios is
acceptable under IBC 903.3.1.2.1. However, NFPA #13 systems are a different
matter and after searching the IBC I see no reference allowing them unless
the framing is sheathed - which I think started in the '06 ed. of IBC since
I can't find it in the '03.
   
   
   
  Cliff,
   
  Darcy calcs are only required if you're system is greater than 40 gallons.
Anything bigger than that should probably be a dry system anyway. :-)
   
  -B-
   
  
Cliff Whitfield <[EMAIL PROTECTED]> wrote:
  Another problem with going AF is now we have to use Darcy Weisbach for
calculations which then opens an additional can of worms.

Cliff
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, February 22, 2008 10:50 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

Correct me if I am wrong, but if the sidewalls are not acceptable under a
small deck, etc. then the only options are antifreeze or dry systems with
upright sprinklers? I understand what you are saying but in practical fact;
is it worth it? If we go antifreeze, we can stay within the residential
boundaries, but going dry opens other issues. 

Can we get the manufacturers to test and list a dry sidewall head for these
uses?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Friday, February 22, 2008 9:31 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

There are two issues with a sprinkler. Those are sensitivity and
distribution. The sidewall sprinklers must be tested to insure that they
provide the appropriate sensitivity and distribution in distribution tests
(RDD & ADD) as well as sensitivity tests and fire tests. I would not think
that having a fire official just deciding one was better than the other is a
really good idea. That smacks of the fire inspector saying he wants
something done just because "he wants it that way". 

Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, February 22, 2008 9:20 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

There seems to be a consensus among the inspector's I know that the sidewall
is better than a pendent in many cases because of the spray pattern. Would
there be a significant difference in the time it takes to fuse the two
different types of heads?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Friday, February 22, 2008 7:47 AM
To: [email protected]
Subject: RE: Dry HSW under open framed 2x's

Check The International Building Code which requires sprinklers protecting
some decks and in that section the IBC allows deviations from NFPA 13 or the
sprinkler listing. Maybe some bleed over into exterior canopies.

Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Thursday, February 21, 2008 5:44 PM
To: [email protected]
Subject: Dry HSW under open framed 2x's

I'm noticing a lot of small exterior canopies being protected with dry
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24"
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question,
they aren't smooth so how are people getting away with this? Smooth being
defined as sructural members being spaced more than 7'-6" o/c. per A3.7.2.

The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's
okay for a pendant why not a HSW? (I'm sure it has to do with the
intracacies of unfamiliar testing and listing requirements of a pendant over
a hsw???)

Any thoughts?

Thx,
-B-


Below are the sections talked about:

NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows: 
(1) Light hazard occupancies with smooth, horizontal or sloped, flat
ceilings
(2) Ordinary hazard occupancies with smooth, flat ceilings where
specifically listed for such use
(3) To protect areas below overhead doors


A.8.15.7 Small loading docks, covered platforms, ducts, or similar small
unheated areas can be protected by dry-pendent sprinklers extending through
the wall from wet sprinkler piping in an adjacent heated area. Where
protecting covered platforms, loading docks, and similar areas, a dry
pendent sprinkler should extend down at a 45 degree angle. The width of the
area to be protected should not exceed 7½ ft (2.3 m). Sprinklers should be
spaced not over 12 ft (3.7 m) apart. (See Figure A.8.15.7.)


A.3.7.2
(3) Smooth Ceiling Construction. The term smooth ceiling construction as
used in this standard includes the following: 
(a) Flat slab, pan-type reinforced concrete
(b) Continuous smooth bays formed by wood, concrete, or steel beams spaced
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or
trusses
(c) Smooth roof or floor decks supported directly on girders or trusses
spaced more than 7½ ft (2.3 m) on center
(d) Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on
metal lath or a combination of materials of equivalent fire-resistive rating
attached to the underside of wood joists, wood trusses, and bar joists
(e) Open-web-type steel beams, regardless of spacing
(f) Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids,
saddles, domes, and long barrel shells
(g) Suspended ceilings of combustible or noncombustible construction
(h) Smooth monolithic ceilings with fire resistance less than that
specified under item (d) and attached to the underside of wood joists, wood
trusses, and bar joists 


---------------------------------
Looking for last minute shopping deals? Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to