Rick,

Require 13 systems in SFDs and you get your wish. Make it apply to
buildings over X sqft and keep 13D for buildings under x sqft. Don't
make 13D something it isn't.

On 2/26/08, Matsuda, Richard <[EMAIL PROTECTED]> wrote:
> There was a "slight" code change between the 1996 and 1999 editions of
>  NFPA-13D, paragraph 4-6, exception #4.
>
>  It changed from stating, "...not required in attics, crawl spaces, and
>  other concealed spaces that are not used or intended for living purposes
>  or storage"...to ..."not required in attics, crawl spaces, and other
>  concealed spaces that are not used or intended for living purposes".
>
>  The committee omitted the words "or storage" which makess it seem that
>  they accept that most attics would be used for storage and sprinklers
>  would not be required. They have since changed the wording again in the
>  2007 edition, par 8.6.5 to state "...and do not contain fuel-fired
>  equipment".
>
>  Some big homes that we have in Dallas have a standard doorway into the
>  attic which is decked with lighting provided, but it's not conditioned
>  space and no walls or ceilings are provided. It's just open to the roof
>  joists. Per the wording of 13D, we allow sprinklers to be omitted.
>
>  I don't agree with this position cause I'd like to have sprinklers in
>  every attic, bathroom, closet and dog house, but until changes are made
>  again I will abide with the committee's decisions.
>  rick matsuda, city of dallas
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
>  Leyton
>  Sent: Tuesday, February 26, 2008 2:55 PM
>  To: [email protected]
>
> Subject: RE: 2nd request 13d attic storage
>
>  But does your attic have a pull-down or fixed stair?   All good points
>  Todd, which underscores how subjective this issue really is.  If it's a
>  storage "room", I'd consider it part of the dwelling unit.  If it's dead
>  space above the ceiling in which the home owner chooses to put stuff,
>  then it quacks like an attic.
>
>  Steve Leyton
>  Protection Design & Consulting
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Todd
>  Williams - FPDC
>  Sent: Tuesday, February 26, 2008 12:31 PM
>  To: [email protected]
>  Subject: Re: 2nd request 13d attic storage
>
>  13D says that sprinklers in attics may be omitted, provided they are
>  not intended for "living purposes". Does storage in an attic space
>  constitute a living purpose? I'm not sure if it does or not. I would
>  think that a case could be made, considering that 13D is a Life
>  Safety System. (My assumption here is that the access to the space is
>  more on the idea of a pull-down stair as opposed to a carpeted
>  staircase.)
>
> _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to