There was a "slight" code change between the 1996 and 1999 editions of
NFPA-13D, paragraph 4-6, exception #4. 

It changed from stating, "...not required in attics, crawl spaces, and
other concealed spaces that are not used or intended for living purposes
or storage"...to ..."not required in attics, crawl spaces, and other
concealed spaces that are not used or intended for living purposes". 

The committee omitted the words "or storage" which makess it seem that
they accept that most attics would be used for storage and sprinklers
would not be required. They have since changed the wording again in the
2007 edition, par 8.6.5 to state "...and do not contain fuel-fired
equipment".

Some big homes that we have in Dallas have a standard doorway into the
attic which is decked with lighting provided, but it's not conditioned
space and no walls or ceilings are provided. It's just open to the roof
joists. Per the wording of 13D, we allow sprinklers to be omitted.

I don't agree with this position cause I'd like to have sprinklers in
every attic, bathroom, closet and dog house, but until changes are made
again I will abide with the committee's decisions.
rick matsuda, city of dallas

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Tuesday, February 26, 2008 2:55 PM
To: [email protected]
Subject: RE: 2nd request 13d attic storage

But does your attic have a pull-down or fixed stair?   All good points
Todd, which underscores how subjective this issue really is.  If it's a
storage "room", I'd consider it part of the dwelling unit.  If it's dead
space above the ceiling in which the home owner chooses to put stuff,
then it quacks like an attic.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Tuesday, February 26, 2008 12:31 PM
To: [email protected]
Subject: Re: 2nd request 13d attic storage

13D says that sprinklers in attics may be omitted, provided they are 
not intended for "living purposes". Does storage in an attic space 
constitute a living purpose? I'm not sure if it does or not. I would 
think that a case could be made, considering that 13D is a Life 
Safety System. (My assumption here is that the access to the space is 
more on the idea of a pull-down stair as opposed to a carpeted
staircase.)