The ability of the sheet to hold a given load is based on the gauge of
the material and the spacing of the structure supporting it.  It's tough
for a manufacturer to assume all conditions and expensive to have UL
test all conditions.  Pay an engineer to test and certify the
installation, then you'll meet code.

Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Friday, February 29, 2008 12:47 PM
To: [email protected]
Subject: RE: Sammy express hangers

I must be missing something with these hangers.  How could they be
listed
for fire protection if they had not been tested in the gauge of steel
that
they are listed for in their tables?  Are we to assume that UL and FM
don't
know how to test hangers to meet the standard?  I thought that when I
looked
on the sammy tables that show a certain style/size sammy screw for a
minimum
gauge steel and a maximum size pipe that this would take into
consideration
all of the requirements of NFPA 13  for hangers.

Maybe someone from Sammy Screws (Textron) is on this forum and can
answer
these questions for us.

Cliff Whitfield, SET
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David M.
Canham
Sent: Friday, February 29, 2008 11:21 AM
To: [email protected]
Subject: RE: Sammy express hangers

Unless the roof or Z-purlin can handle 250 punds plus the pipe the code
has
not been meet.
9.2.1.3.1  Sprinkler piping shall be substantially supported from the
building structure, which must support the added load of the
water-filled
pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging.

Dave Canham
Fire Systems Solutions

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, February 29, 2008 11:26 AM
To: [email protected]
Subject: RE: Sammy express hangers

Dewayne,

The last project, which I think was similar to your situation, we used 
Sammy side-winders on the Z-purlins.  It was an ESFR project and I think

we roughly calculated the load would be about 1.1 lbs/ft2 on average.
We 
did have to check with structural to make sure the point loads could be 
handle for the cross main.  I think they told me that 2-3 lbs is added
for 
miscellaneous loads such as sprinklers, lights, HVAC.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Steve Leyton" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
02/29/2008 10:39 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: Sammy express hangers







There's no one answer Dewayne.   Some roof decks can bear the load, some
can't.    That question should be referred to the project structural
engineer of record.  If the roof has structural concrete on it, which
many do, it can often bear the load of branch piping and arm-overs.
Some are so lightweight, they can't bear even the arm-overs.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, February 29, 2008 7:09 AM
To: [email protected]
Subject: Sammy express hangers

Has anyone run into problems with building inspectors when trying to use
the Sammy express hanger in the roof deck.  I have one telling me that
"the metal decking is designed for the roofing materials and designed
loads (rain, snow, etc.). That the design did not include other loads."
Is this true? 
Thanks,
Dewayne 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)