Right; essentially it's a combination manual-wet standpipe system and we've designed a few this way that required pumps to meet the sprinkler demand, but where automatic water supply isn't required of the standpipe system. Keep in mind that if you have Class II or III standpipes with hose, there should be an automatic water supply capable of meeting the Class II demand as it may apply and be enforced by the local AHJ.
Also, wearing gloves will help with the splinters. And what's up with Asanti Samuels going to Philly? Is the Patsy locker room THAT bad? Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Justin Reid Sent: Friday, February 29, 2008 4:48 PM To: [email protected] Subject: RE: Dumb Question maybe Tom, Your building is equipped with a manual wet standpipe system. NFPA 14 generally only requires your system to be automatic (capable of supplying the demand independent of the fire department pumper truck) when the building is considered a high-rise. So according to NFPA 14 you would be able to size the fire pump to meet the sprinkler demand and not the hose demand. There may be other situations that would require you to provide an automatic system that may be found in your building code. I don't want to say for sure that you don't need one without knowing all of the details of your building, system, local jurisdiction; but, in your search for an answer, you should be looking for a designation between being required to provide an automatic system or a manual system. Good luck. Justin D. Reid, P.E. Project Engineer RLH Fire Protection 3430 Unicorn Road Bakersfield, CA 93308 Office: (661) 410-1350 Cell: (213) 798-0251 Fax: (661) 322-6816 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Friday, February 29, 2008 4:02 PM To: [email protected] Subject: Dumb Question maybe I just did a standpipe test today. Mixed-use building, mid-rise, mercantile on the ground floor, residential above 2-5. 56' sidewalk to parapet. It has a fire pump but the pump is only sized for the sprinklers (400 GPM). It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13). We had to get a pumper truck for the standpipe test, 2 standpipes to flow. I had wtf when I went there 2 weeks ago to look around, they (contractor) said "not our design, we just installed it", and "Plans were approved". Is there a statute I'm unaware of that says in an installation like this you have the option to size the fire pump to meet the sprinkler demand and not the hose demand? Nothing I know of in our local Building Code or Ordinances. Scratching my head and getting splinters. Tom Duross Go Red Sox _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)