Right;  essentially it's a combination manual-wet standpipe system and
we've designed a few this way that required pumps to meet the sprinkler
demand, but where automatic water supply isn't required of the standpipe
system.  Keep in mind that if you have Class II or III standpipes with
hose, there should be an automatic water supply capable of meeting the
Class II demand as it may apply and be enforced by the local AHJ.   

Also, wearing gloves will help with the splinters.   And what's up with
Asanti Samuels going to Philly?  Is the Patsy locker room THAT bad?

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Justin
Reid
Sent: Friday, February 29, 2008 4:48 PM
To: [email protected]
Subject: RE: Dumb Question maybe

Tom,

Your building is equipped with a manual wet standpipe system. NFPA 14
generally only requires your system to be automatic (capable of
supplying the demand independent of the fire department pumper truck)
when the building is considered a high-rise. So according to NFPA 14 you
would be able to size the fire pump to meet the sprinkler demand and not
the hose demand. 

There may be other situations that would require you to provide an
automatic system that may be found in your building code. I don't want
to say for sure that you don't need one without knowing all of the
details of your building, system, local jurisdiction; but, in your
search for an answer, you should be looking for a designation between
being required to provide an automatic system or a manual system. Good
luck. 


Justin D. Reid, P.E.
Project Engineer
RLH Fire Protection 
3430 Unicorn Road
Bakersfield, CA 93308
Office: (661) 410-1350
Cell: (213) 798-0251
Fax: (661) 322-6816
[EMAIL PROTECTED] 
 

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Friday, February 29, 2008 4:02 PM
To: [email protected]
Subject: Dumb Question maybe

I just did a standpipe test today.
Mixed-use building, mid-rise, mercantile on the ground floor,
residential
above 2-5.  56' sidewalk to parapet.
It has a fire pump but the pump is only sized for the sprinklers (400
GPM).
It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13).
We had to get a pumper truck for the standpipe test, 2 standpipes to
flow.
I had wtf when I went there 2 weeks ago to look around, they
(contractor)
said "not our design, we just installed it", and "Plans were approved".

Is there a statute I'm unaware of that says in an installation like this
you
have the option to size the fire pump to meet the sprinkler demand and
not
the hose demand?  Nothing I know of in our local Building Code or
Ordinances.

Scratching my head and getting splinters.

Tom Duross
Go Red Sox


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to