I just did a standpipe test today. Mixed-use building, mid-rise, mercantile on the ground floor, residential above 2-5. 56' sidewalk to parapet. It has a fire pump but the pump is only sized for the sprinklers (400 GPM). It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13). We had to get a pumper truck for the standpipe test, 2 standpipes to flow. I had wtf when I went there 2 weeks ago to look around, they (contractor) said "not our design, we just installed it", and "Plans were approved".
Is there a statute I'm unaware of that says in an installation like this you have the option to size the fire pump to meet the sprinkler demand and not the hose demand? Nothing I know of in our local Building Code or Ordinances. Scratching my head and getting splinters. Tom Duross Go Red Sox _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)