Tom,

The Mass Code is confusing on this issue. Section 914.1 states that when standpipes are required to be installed, they shall be automatic wet type. This would mean that they would need to meet the flow and pressure demands with the on site supply. However, section 914.3 Exception states that the residual pressures are not required to met if the building is under 70 feet high, effectively making it a manual wet standpipe. I think an interpretation may be in order.

Todd



At 07:01 PM 2/29/2008, you wrote:
I just did a standpipe test today.
Mixed-use building, mid-rise, mercantile on the ground floor, residential
above 2-5.  56' sidewalk to parapet.
It has a fire pump but the pump is only sized for the sprinklers (400 GPM).
It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13).
We had to get a pumper truck for the standpipe test, 2 standpipes to flow.
I had wtf when I went there 2 weeks ago to look around, they (contractor)
said "not our design, we just installed it", and "Plans were approved".

Is there a statute I'm unaware of that says in an installation like this you
have the option to size the fire pump to meet the sprinkler demand and not
the hose demand?  Nothing I know of in our local Building Code or
Ordinances.

Scratching my head and getting splinters.

Tom Duross
Go Red Sox


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to