Tom,

The Mass Code is confusing on this issue. Section 914.1 states that
when standpipes are required to be installed, they shall be automatic
wet type. This would mean that they would need to meet the flow and
pressure demands with the on site supply. However, section 914.3
Exception states that the residual pressures are not required to met
if the building is under 70 feet high, effectively making it a manual
wet standpipe. I think an interpretation may be in order.

Todd

Todd, I'm very familiar with that section BUT these are not manual
standpipes if they're connected to an automatic water supply.  If they were
separate, OK I can see the justification but they're not.  They're connected
to the same supply as the sprinklers and the fire (sprinkler) pump.  My
understanding of that section says if I have enough street pressure to
satisfy the sprinklers, I don't have to install a pump just for the hose
demand (only class 3 in MA).  But, these guys designed and installed a fire
pump connected to two combination class 3 standpipes and only sized it for
the sprinklers.  I don't think that's right.

Tom