It is a two hour concrete block firewall. There is a fire rated
door in the
corridor, which will constitute the horizontal exit. Hose stations are
provided on both sides. Are separate zones being provided by others
for
similar buildings? I know I will have to follow my building code,
but what
is the industry practice?
Thanks,
Tony
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: March 10, 2008 7:51 AM
To: [email protected]
Subject: Re: Horizontal Exits
IS it a firewall or a rated partition? A firewall can often be
identified
by what looks like two walls butted together since they have to remain
standing with structural collapse on either side(kinda like seismic
joints
for structural steel). Haven't looked closely lately at the
penetration
allowance but you shouldn't be seeing doorways. Must confess, I
haven't
focused on construction issues in a long time but such basic
tenants should
be the same as in my Flintstone days.
If it is a firewall, each has a separate floor area because they are
separate buildings with common walls. So, are separate zones
required in
separate buildings?
Just because the owner/GC is using an accelerated design as you go
format
doesn't mean the the architect/engineer of record are exempt from such
trivial issues.
Roland
On Mar 8, 2008, at 11:00 AM, A.P.Silva wrote:
I have another question related to this issue.
A four storey residential buiding, having 30,000 sq.ft. building
area,
has two firewalls, splitting it to 3 compartments. The City is saying
each compartment (approx. 10,000 sq.ft.) needs a separate zone.
As per building code:
The annunciator shall have separate zone indication of the actuation
of the alarm initiating devices in each "floor area" so that the area
of coverage for each zone is neither (a) more than one storey, nor
(b)
more than the system area limits as specified in NFPA 13.
"Floor area" is defined as any space between the exterior walls and
any required fire walls.
I'm saying the zone indicatipon must be obtained by another alarm
initiating device. Not sprinkler flow switch. The problem is the
building code also permits deletion of heat detectors, if the
building
is sprinklered.
So that
leaves only manual pull stations and sprinklers.
I know to reply, the applicable building code has to reviewed in its
entirety. But most building codes are similar. My question is, are
there any other jurisdiction that would require sprinkler zoning for
each compartment?
Tony
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jamie
Seidl
Sent: March 7, 2008 3:02 PM
To: '[email protected]'
Subject: Re: Horizontal Exits
Yup in the NC 2006 IBC we have that same exception.
----- Original Message -----
From: [EMAIL PROTECTED]
<[EMAIL PROTECTED]>
To: [email protected]
<[email protected]>
Sent: Fri Mar 07 16:58:39 2008
Subject: RE: Horizontal Exits
What Jamie said. An exit through a fire-rated separation; the reason
for Class I connections on both sides is that one side is presumed to
be separated and safe from the fire on the other.
Remember though, that if you are considering said connections
based on
prescriptive code requirements, you should check out whether there's
an exception your state's adopted version of the IBC, section 905.4
(Location of Class I standpipe hose connections. The new California
version, based on
2006 includes the following for location of connections, which I
think
is straight IBC without amendments:
905.4.2 On each side of the wall adjacent to the exit opening of a
horizontal exit.
Exception: Where floor areas adjacent to a horizontal exit are
reachable from exit stairway hose connections by a 30-foot hose
stream
from a nozzle attached to 100 feet of hose, a hose connection shall
not be required at the horizontal exit.
Steve Leyton
Protection Design & Consulting
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jamie
Seidl
Sent: Friday, March 07, 2008 1:07 PM
To: [email protected]
Subject: RE: Horizontal Exits
Chap 10 of the 2003 IBC.
Exit, Horizontal. A path of egress travel from one building to an
area in another building on approximately the same level, or a
path of
egress travel through or around a wall or partition to an area on
approximately the same level in the same building, which affords
safety from fire and smoke from the area of incidence and areas
communicating therewith.
(Think 2 hr fire walls, double doors in corridors with magnetic
holders).
Jamie Seidl
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Richard
Battershell
Sent: Friday, March 07, 2008 3:45 PM
To: [email protected]
Subject: Horizontal Exits
Class I standpipes as per NFPA 14 7.3.2 (2)2004 ed. requires hose
connections be provided "On each side of the wall adjacent to the
exit
openings of horizontal exits". What constitutes a horizontal exit?
Thanks for the help.
Richard Battershell
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED] (Put the word unsubscribe in the subject
field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED] (Put the word unsubscribe in the subject
field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]