I agree with your assessment.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Craig Rauch
> Sent: Monday, April 14, 2008 7:15 AM
> To: [email protected]
> Subject: TJI Concealed spaces
> 
> 
> 
> I am looking at plans for a building that has 20" TJI Composite Wood
> Joist Construction between the floors. The building is to be equipped
> with an NFPA 13 system to the 2002 edition.
> 
> The sprinkler company is attempting to use Section 8.14.1.2.5 to avoid
> sprinkling the combustible concealed spaces.
> 
> My reaction is that this exception would not apply to this situation,
> and that 8.14.1.2.6 would apply if this is the direction they want to
> go.
> 
> I am looking for a bit of input so I am sure I am on the right track.
> 
> Craig Rauch
> Plans Examiner
> Washington Township Fire Department
> _______________________________________________