I agree with your assessment. Ed Kramer Littleton, CO
> -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Craig Rauch > Sent: Monday, April 14, 2008 7:15 AM > To: [email protected] > Subject: TJI Concealed spaces > > > > I am looking at plans for a building that has 20" TJI Composite Wood > Joist Construction between the floors. The building is to be equipped > with an NFPA 13 system to the 2002 edition. > > The sprinkler company is attempting to use Section 8.14.1.2.5 to avoid > sprinkling the combustible concealed spaces. > > My reaction is that this exception would not apply to this situation, > and that 8.14.1.2.6 would apply if this is the direction they want to > go. > > I am looking for a bit of input so I am sure I am on the right track. > > Craig Rauch > Plans Examiner > Washington Township Fire Department > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
