8.14.1.2.5 does not apply to composite wood joist, you must use 8.14.1.2.6. If you'll look at the definitions in the 2007 handbook there is a difference between Wood Joist Construction, which deals with solid wood joists, and Composite wood joist construction which deals with TJI's. I believe that the committee ment for 8.14.1.2.5 to apply only to "Wood Joist Construction" or Solid wood joists, and 8.14.1.2.6 to apply to Composite wood joist construction or TJI's. "Concealed spaces formed by ceilings attached to composite wood joist construction either directly or ----" This is pretty clear that this is what you should use for composite joist. Just because it's after 8.14.1.2.5 doesn't mean that 5 has priority over 6. Just that they apply differently to differing situations that are "Concealed spaces not requiring sprinkler protection"
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Craig Rauch" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, April 14, 2008 7:14 AM
Subject: TJI Concealed spaces




I am looking at plans for a building that has 20" TJI Composite Wood Joist Construction between the floors. The building is to be equipped with an NFPA 13 system to the 2002 edition.

The sprinkler company is attempting to use Section 8.14.1.2.5 to avoid sprinkling the combustible concealed spaces.

My reaction is that this exception would not apply to this situation, and that 8.14.1.2.6 would apply if this is the direction they want to go.

I am looking for a bit of input so I am sure I am on the right track.

Craig Rauch
Plans Examiner
Washington Township Fire Department
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to