NFPA 13 2002 ed 8.16.4.6.1 Means SHALL be provided downstream of all
backflow prevention valves for flow test at system demand.
2007 ed 8.17.4.6.1 states the same thing.
System acceptance 16.2.5.1 The backflow prevention assembly SHALL be
forward flow tested to ensure proper operation.
A 8.16.4.6.1 gives some ideas how to accomplish this.
Required? appears so
Thom McMahon wrote:
Gentlemen, please remember that 25 only requires the full forward flow if
the provisions for it have been made in the riser or system. It does not
require that you fail the system, or require the installation of full
forward flow appliances it they don't exist. IF they are there use them and
test the backflow, if not simply test the backflow as per ASSE or as
required by the water AHJ and move on. (It's the same old question with all
installations, Did the AHJ allow this at the time, or was this just an
installation violation. The assumption is always that the AHJ allowed it, to
do otherwise, if the owner says there have been no changes to the system
would make inspections a confrontational situation, which would not improve
the system reliability.)
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, May 30, 2008 1:45 PM
To: [email protected]
Subject: RE: Full-flow backflow test
That's a good logical argument - but it involves too many steps to be
enforced 'round here. Kind of like a political argument that can't fit on a
bumper sticker. So if it's not enforced, the contractors aren't going to add
the costs (a criticism of the system, not the contractors).
As to section 8.17.4.6.1 ('08 ed): It does not require a test outlet - it
requires a means of full-flow testing, which would be satisfied by someone
saying that they'll just replace the check valve with a 4 in.
elbow and pipe it to the outside on the day of testing...somehow.
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David Autry
Sent: Friday, May 30, 2008 2:12 PM
To: [email protected]
Subject: Full-flow backflow test
It's required in 25, which is referenced in 13. So that makes it a
requirement of 13 (NFPA 13, 2002 edition, 2.1)
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Friday, May 30, 2008 1:58 PM
To: [email protected]
Subject: RE: 200 psi test for components rated 175
Seeing as the backflow isn't a fire appliance, it makes sense that it's
outside the scope of 13. I'm pretty sure the "full forward flow test"
is a jurisdictional agency thing, i.e. NAVFAC or the serving water
company. So fire officials might require it too - for peace of mind
perhaps?
BTW, you mitigate the clapper issue by turning the FDC body upside down.
Duh.
Steve Leyton
Protection Design & Consulting
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, May 30, 2008 11:33 AM
To: [email protected]
Subject: RE: 200 psi test for components rated 175
Don't most FDCs include clappers? How do you backwards flow out an FDC with
clappers? And what do you do when the system has a high demand volume - say
over 500 gpm? You'll have a tough time flowing it out an FDC even without
clappers.
Seems it's the responsibility of the engineer of record (when they're
present) to require the test outlet so the owner has a means of meeting the
requirements of NFPA 25 - even if the inspectors never end up testing the
backflow.
When there is not an engineer of record, and a contractor is asked to
design/install a system per code, I don't believe there is any language in
NFPA 13 that would force a contractor to install the test outlet.
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 12:23 PM
To: [email protected]
Subject: Re: 200 psi test for components rated 175
Yep, that could be the reason it is shown.
Yea Matt, sorta trick question, We have installed a few wall hydrants at
Military bases.
Funny thing is that they do there own inspections and they don't
follow NFPA 25 that requires an annual forward flow on the backflows. So the
only systems in our area that do have them , are not being used.
OK while we are at it, how many NFPA 25 inspectors perform the
required forward flow test annually?
-
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta ;GA;30907
email;internet:[EMAIL PROTECTED]
title:Project Manager
tel;work:706-650-7730
tel;fax:706-650-7731
tel;cell:706-412-1281
url:www.firetecheng.com
version:2.1
end:vcard
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)