That's my understanding also. These things are designed to open a
little lots of times and if not fully opened regularly they might not
fully open when needed. I do agree that a main drain is probably
sufficient for low flow systems but how much can you actually flow
through a 2" pipe. A quick search shos my 2" schd 40 black steel table
stops at 335 gpm.

On Fri, May 30, 2008 at 5:13 PM, scott mitchell <[EMAIL PROTECTED]> wrote:
> I don't think the intent is to measure the pressure drop across the device.  
> Based on what I've read and what I understand to be the intent of the minimum 
> standard, if you measure 400 gpm and the system demand is 379, then you've 
> conducted a full flow test at system demand.
>
> UL does not test the assembly for proper operation after an extended period 
> of time with no water movement.  So, this is a means of exercising the 
> assembly and showing that the demand flow can make it through.
>
> While not prescribed by 13 or 25, prudent ITM procedures would include 
> measuring the pressure drop across the device.
>
> Scott Mitchell
>
>
>