Like everything else in the "STANDARD" (not Code) It's only required if the AHJ say's it is. We have jurisdictions here in the west,( where water law has more lawyers than any other kind,) and water authorities don't want the full forward flow ability to be installed, because it uses to much water on a connection that's un-metered. Usually the Fire AHj agrees.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Friday, May 30, 2008 3:14 PM To: [email protected] Subject: Re: Full-flow backflow test NFPA 13 2002 ed 8.16.4.6.1 Means SHALL be provided downstream of all backflow prevention valves for flow test at system demand. 2007 ed 8.17.4.6.1 states the same thing. System acceptance 16.2.5.1 The backflow prevention assembly SHALL be forward flow tested to ensure proper operation. A 8.16.4.6.1 gives some ideas how to accomplish this. Required? appears so > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)