Like everything else in the "STANDARD" (not Code) It's only required if the
AHJ say's it is. We have jurisdictions here in the west,( where water law
has more lawyers than any other kind,) and water authorities don't want the
full forward flow ability to be installed, because it uses to much water on
a connection that's un-metered. Usually the Fire AHj agrees.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 3:14 PM
To: [email protected]
Subject: Re: Full-flow backflow test

NFPA 13 2002 ed 8.16.4.6.1  Means SHALL be provided downstream of all
backflow prevention valves for flow test at system demand.
2007 ed 8.17.4.6.1 states the same thing.
  System acceptance 16.2.5.1 The backflow prevention assembly SHALL be
forward flow tested to ensure proper operation.
  A 8.16.4.6.1 gives some ideas how to accomplish this.

Required?  appears so