A 2" Nozzle with a 2.00" ID will flow 830 Gpm @ 60 Psi Pitot a 21/2" nozzle
will flow 1300 Gpm @ 60 Psi pitot

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Friday, May 30, 2008 7:14 PM
To: [email protected]
Subject: Re: Full-flow backflow test

That's my understanding also. These things are designed to open a little
lots of times and if not fully opened regularly they might not fully open
when needed. I do agree that a main drain is probably sufficient for low
flow systems but how much can you actually flow through a 2" pipe. A quick
search shos my 2" schd 40 black steel table stops at 335 gpm.

On Fri, May 30, 2008 at 5:13 PM, scott mitchell <[EMAIL PROTECTED]> wrote:
> I don't think the intent is to measure the pressure drop across the
device.  Based on what I've read and what I understand to be the intent of
the minimum standard, if you measure 400 gpm and the system demand is 379,
then you've conducted a full flow test at system demand.
>
> UL does not test the assembly for proper operation after an extended
period of time with no water movement.  So, this is a means of exercising
the assembly and showing that the demand flow can make it through.
>
> While not prescribed by 13 or 25, prudent ITM procedures would include
measuring the pressure drop across the device.
>
> Scott Mitchell
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to