Back to the "Main Drain Test" (Just as a note, most of our systems will flow
full design, even for OH II thru a 2" main drain connection. If you install
the main drain you've provided the ability to full forward flow the backflow
device.) Static Psi over 120 with residual above 100 flowing over 3500 Gpm.
Our normal. Those big hill's called the "Rockies" make reducing pressure our
problem. A PRV station fails and we increase Psi by more than 50%.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Friday, May 30, 2008 3:26 PM
To: [email protected]
Subject: Re: Full-flow backflow test

Gregg,

I was addressing older systems per NFPA 25 built to a prior code where there
is no means to test full-flow and no requirement to add such a means. Even
in these cases you have to forward flow as best you can.