Hello Dewayne,

I know of at least 1 check valve that has a "Test Cap" listed in their parts 
breakdown. Just the bolt on cover without a clapper (It was in a spec a couple 
of years ago). We use the CV=1F a lot and I got some replacement covers for the 
guys to use for testing.

Monday, June 2, 2008, 7:48:01 AM, you wrote:

> We have one AHJ that won't allow us to touch the check valve after the
> 200PSI test because we are "altering" the system that has been tested.
> He makes all the contractors install a "bypass" around with FDC check
> valve and install a butterfly valve in-line to test the BFP without
> having to remove the check valve or it's clapper.  Has anyone heard of
> this not being allowed in 25 or is the AHJ just making a reach?
> Thanks,
> Dewayne 

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
> Leyton
> Sent: Friday, May 30, 2008 1:58 PM
> To: [email protected]
> Subject: RE: 200 psi test for components rated 175

> Seeing as the backflow isn't a fire appliance, it makes sense that it's
> outside the scope of 13.   I'm pretty sure the "full forward flow test"
> is a jurisdictional agency thing, i.e. NAVFAC or the serving water
> company.   So fire officials might require it too - for peace of mind
> perhaps?

> BTW, you mitigate the clapper issue by turning the FDC body upside down.
> Duh.

> Steve Leyton
> Protection Design & Consulting


> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Mark
> Sornsin
> Sent: Friday, May 30, 2008 11:33 AM
> To: [email protected]
> Subject: RE: 200 psi test for components rated 175

> Don't most FDCs include clappers?  How do you backwards flow out an FDC
> with clappers? And what do you do when the system has a high demand
> volume - say over 500 gpm? You'll have a tough time flowing it out an
> FDC even without clappers.

> Seems it's the responsibility of the engineer of record (when they're
> present) to require the test outlet so the owner has a means of meeting
> the requirements of NFPA 25 - even if the inspectors never end up
> testing the backflow.

> When there is not an engineer of record, and a contractor is asked to
> design/install a system per code, I don't believe there is any language
> in NFPA 13 that would force a contractor to install the test outlet.

> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc. 
> Fargo, ND
> 701.280.8591
> [EMAIL PROTECTED] 
>  

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
> Sent: Friday, May 30, 2008 12:23 PM
> To: [email protected]
> Subject: Re: 200 psi test for components rated 175

> Yep, that could be the reason it is shown.

> Yea Matt, sorta trick question, We have installed a few wall hydrants at
> Military bases.
>         Funny thing is that they do there own inspections and they don't
> follow NFPA 25 that requires an annual forward flow on the backflows. So
> the only systems in our area that do have them , are not being used.
>         OK while we are at it, how many NFPA 25 inspectors perform the
> required forward flow test annually?


> -
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston CET
Coastal Fire Protection
 Coastal                            mailto:[EMAIL PROTECTED]