We have one AHJ that won't allow us to touch the check valve after the 200PSI test because we are "altering" the system that has been tested. He makes all the contractors install a "bypass" around with FDC check valve and install a butterfly valve in-line to test the BFP without having to remove the check valve or it's clapper. Has anyone heard of this not being allowed in 25 or is the AHJ just making a reach? Thanks, Dewayne
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Friday, May 30, 2008 1:58 PM To: [email protected] Subject: RE: 200 psi test for components rated 175 Seeing as the backflow isn't a fire appliance, it makes sense that it's outside the scope of 13. I'm pretty sure the "full forward flow test" is a jurisdictional agency thing, i.e. NAVFAC or the serving water company. So fire officials might require it too - for peace of mind perhaps? BTW, you mitigate the clapper issue by turning the FDC body upside down. Duh. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin Sent: Friday, May 30, 2008 11:33 AM To: [email protected] Subject: RE: 200 psi test for components rated 175 Don't most FDCs include clappers? How do you backwards flow out an FDC with clappers? And what do you do when the system has a high demand volume - say over 500 gpm? You'll have a tough time flowing it out an FDC even without clappers. Seems it's the responsibility of the engineer of record (when they're present) to require the test outlet so the owner has a means of meeting the requirements of NFPA 25 - even if the inspectors never end up testing the backflow. When there is not an engineer of record, and a contractor is asked to design/install a system per code, I don't believe there is any language in NFPA 13 that would force a contractor to install the test outlet. Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND 701.280.8591 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Friday, May 30, 2008 12:23 PM To: [email protected] Subject: Re: 200 psi test for components rated 175 Yep, that could be the reason it is shown. Yea Matt, sorta trick question, We have installed a few wall hydrants at Military bases. Funny thing is that they do there own inspections and they don't follow NFPA 25 that requires an annual forward flow on the backflows. So the only systems in our area that do have them , are not being used. OK while we are at it, how many NFPA 25 inspectors perform the required forward flow test annually? - _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)