Todd,
I've never been able to calc 800 gpm through 1", but as I believe I have
heard Roland say at least once the velocity issue is a self correcting
phenom.  At a certain point in your system no matter how much pressure you
throw at it, the velocity is going to check itself by causing pipe to be
upsized.  I do not like to see high velocities in my calcs (over 32 fps),
but on occasion it does happen.  I can't see where lowering velocity, as an
example, from 37 fps down to 32 fps is justified by increasing pipe size on
a job that has a couple of thousand feet of pipe.  The sprinkler system will
still function correctly at 37 fps as it would at 32 fps.  The only
difference I see is that the 32 fps system is now going to cost someone a
whole bunch more than the 37 fps system.  Back to Pu = $S.

bk

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Monday, June 02, 2008 9:51 AM
To: [email protected]
Subject: Re: High velocities

It sounds like I'm the only one out there not designing systems with Mach 3
velocities. There has to physically be some upper limit to what a pipe can
carry. You're not going to get 800 gpm through a piece of 1", even though
you can calculate the friction loss with HW. 
Where is the practical limit? (Joe may be able to shed some insight. 
hint, hint....)


At 11:27 AM 6/2/2008, you wrote:
>The formula that I was taught some time back is, Pu = $s (pressure 
>unused equals dollars spent).
>
>BK
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of 
>Fletcher, Ron
>Sent: Monday, June 02, 2008 9:12 AM
>To: [email protected]
>Subject: RE: High velocities
>
>Burn it up!
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Chris 
>Cahill
>Sent: Monday, June 02, 2008 7:47 AM
>To: [email protected]
>Subject: High velocities
>
>
>
>A question for where there is healthy pressures.  Around here 60 is 
>considered high.  I know places with 28 static.
>  Got a OHII system that needs to be changed to EXII.
>  That's not negotiable.  It's a 40 yo pipe schedule system.  That 
>appears to be in good shape.  The BL need to be replaced for 100 sq.ft.
>but the main even the last 12'
>of 2.5", 25' of 3" and 36' of 3.5" can fly without being replaced.  The 
>openings are where I need them.  There is a FP with about 140 psi at 
>the 900gpm demand.  The "problem"
>is the velocities in one segment of pipe are just about 40 (last piece 
>of 3") and about 30 in the 3.5".  I quote problem because I know 13 has 
>no limit, this is not FM.
>  There is still better than 15 psi safety.
>
>So the question is where you have pressure do you typically burn it up 
>with small pipe size at the cost of velocities getting high or do you 
>leave a lot of safety?
>  Again not FM and OK per 13.
>
>Any thoughts on why this is a bad idea?  It's easy to say just pull the 
>offending pipe.  In reality though you all know the competitive market 
>and spending owners money.
>
>
>Chris Cahill, P.E.
>Fire Protection Engineer
>Sentry Fire Protection, Inc.
>
>763-658-4483
>763-658-4921 fax
>
>Email: [EMAIL PROTECTED]
>
>Mail: P.O. Box 69
>         Waverly, MN 55390
>
>Location: 4439 Hwy 12 SW
>               Waverly, MN 55390

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to