Re-posting my previous question, somewhat re-phrased. If a wall had a
valence or shelf 20" below a sprinkler head, is it a potential obstruction,
as per 13?

Tony

               ________     _______________I____
                       I   I
                       I   I                sprinkler
                       I   I 20"
                       I   I
                       I   I____________
                       I                I
                       I    ____________I 
                       I   I
                       I   I<---26------>
                       I   I
                       I   I
                       I   I
                       I   I
                       I   I

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: June 2, 2008 1:01 PM
To: [email protected]
Subject: Obstruction

Shopping mall with CRU's on one side and mall corridor on the other. At the
lease line there is an "L" shaped valence that drops 20 inches (vertical, at
the lease line)from the ceiling and runs 26 inches (horizontal) towards the
corridor. Typically there is no wall between the CRU's and the mall. Is this
valence an obstruction to the sprinklers at the high ceiling level?

My first solution was to space the sprinklers on both sides of the valence
(CRU side and mall side), so that they cover up to the centre-line of the 26
inch wide valence. However, the sprinklers on the CRU side will change for
tenant renovations, and the mall owner will not be able to enforce the
tenant to provide coverage beyond the lease line. Hence, the sprinkler in
the corridor side has to cover up to the lease line. Are the sprinklers in
the corridor unobstructed due to the valence being more than 18 inches below
the sprinkler deflector, or is the valence an obstruction, and possibly
requiring sprinklers below the valence?

Tony

                                   concealed sprinkler
                _______    __________________I_______ceiling
                      I   I
                      I   I
                      I   I             <-6"->
                      I   I 20"
                      I   I
                      I   I_____________
                      I                 I
                      I_________________I

                      <------ 26 ------->


                      I<--- lease line
                 
          CRU's           Mall corridor        

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to