A typical data center with the amount of plastics in the equipment,
various paper products, furnishings, etc. can easily exceed light
hazard.  So you need to know what all is going in the area.

Then add data storage especially if it's 9-track mag tape on movable or
fixed racks or something similar and you have even more to deal with.

Check out NFPA 75 to start with, that will lead back to NFPA 13, or NFPA
2001, or other standards depending on the method of protection you
decide upon.  You can also look at FMDS 5-32.  

There are code issues with the location and ventilation of battery
charging systems, especially if they are lead-acid batteries, gel-cell
or glass mat batteries are not as big an issue but still need to be
addressed from a building code separation and mechanical standpoint.  

Of the data centers I've done lately none have been less than 0.15
density.  0.20 was the highest as required by the underwriter.  There
have been wet systems, FM-200, FM-200/wet, single and double interlocked
pre-action systems.  Each was specifically dictated by the owner or
underwriter.   

If I didn't have an owner or underwriter with a preference I'd recommend
automatic wet, with area smoke detection cross zoning both photoelectric
and ionization detectors.  The smokes give an early warning to an event
giving occupants a chance to rectify the situation manually before the
sprinklers go off.  Provide portable CO2 fire extinguishers per NFPA 10.

If a pre-action was required I wouldn't waste the time going with more
than single interlock.  The delay in operation of the system could
result in additional unrecoverable damage. 

Last choice would be FM-200 BUT with automatic wet sprinklers installed
as backup.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Tuesday, June 03, 2008 10:29 AM
To: SprinklerFORUM
Subject: Data Center

Can anyone point me in the right direction for design criteria for a
data center? All we know so far is I have data storage and battery racks
about 7'
tall. This room is roughly 15,000 sq. ft.

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to