Typical is double interlock pre action, as the minimum, then based upon
insurance and owner requirements, the value of data, the allowable down time
(There are Data Center standards for how many hours per year they can be
down , on a sliding scale. In the most rigorous you wouldn't have preaction,
it would be all gas FM200 ect. In between you have both, and as I said at
the bottom end you have just pre action.

It's all about money (Value) and time. (What it takes to get back up and
running.)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Tuesday, June 03, 2008 8:29 AM
To: SprinklerFORUM
Subject: Data Center

Can anyone point me in the right direction for design criteria for a data
center? All we know so far is I have data storage and battery racks about 7'
tall. This room is roughly 15,000 sq. ft.

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to