I'm with Craig on this pre-action issue. Why at all, but if the owner insists what advantage do you get from double interlock? Double interlocks are primarily useful for warehouse size freezers where an accidental filling of the pipes is unwanted because the water will freeze. Are we mistakingly calling single interlock with supervisory air a double interlock?
On Tue, Jun 3, 2008 at 8:58 AM, Thom McMahon <[EMAIL PROTECTED]> wrote: > Typical is double interlock pre action, as the minimum, then based upon > insurance and owner requirements, the value of data, the allowable down time > (There are Data Center standards for how many hours per year they can be > down , on a sliding scale. In the most rigorous you wouldn't have preaction, > it would be all gas FM200 ect. In between you have both, and as I said at > the bottom end you have just pre action. > > It's all about money (Value) and time. (What it takes to get back up and > running.) > > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: 970-879-7952 > Fax: 970-879-7926 > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell > Sent: Tuesday, June 03, 2008 8:29 AM > To: SprinklerFORUM > Subject: Data Center > > Can anyone point me in the right direction for design criteria for a data > center? All we know so far is I have data storage and battery racks about 7' > tall. This room is roughly 15,000 sq. ft. > > Best regards, > > Joe Burtell, SET, CFPS > Burtell Fire Protection, Inc. > Phone: 406.652.7697 > Fax: 406.652.7743 > Cell: 406.861.4507 > Email: [EMAIL PROTECTED] > Web Site: http://www.burtellfire.com > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)