Well, how about this one, which I just picked up from a fire department
website today, here in Southern California:
"Sprinkler heads in the garage shall be protected against damage by
approved guards"
This has been interpreted to require that recessed sprinklers must have
head guards installed.
There are none listed for recessed sprinklers.
Doesn't phase them a bit. When I asked how it was to be resolved, the
answer was "That's your problem, not mine."
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Todd Williams - FPDC wrote:
My favorite so far is the AHJ who required a stamped letter stating
that the public supply could provide the required flow (about 36 gpm)
for the 10 minute duration.
At 11:23 AM 6/11/2008, you wrote:
Hello Thom,
I am working on my first 13D system now. The problem I am having is
the water purveyor will not install a tap of less than 4" (they can be
forced to a 2 1/2" by their "policy") when there is a fire system
involved.
THEN The building department wants it reviewed to 13R as they have never
dealt with a 13D system. It is on the third review...
Wednesday, June 11, 2008, 10:59:04 AM, you wrote:
> Just wondering if others are seeing excessive water demands for 13D
systems
> by AHJ's? We see 4 head design requirements with 0.10 Gpm/Sf for slope
> ceilings over 8/12. This is the same as a 13 system in residential
> occupancy, yet these two systems are not intended to provide the
same level
> of protection.
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel: 970-879-7952
> Fax: 970-879-7926
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
--
Best regards,
Charles Thurston
mailto:[EMAIL PROTECTED]
Coastal Fire Protection
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)