Charles,
as a local AHJ, I might approve your entry vestibule without sprinklers
on a case-by-case basis provided I had more information.

In the past, I have approved an unsprinklered totally glass vestibule,
about 5 x 12-feet size, which protruded into a building lobby. The lobby
was fully sprinklered and open to the 2nd floor so there were sprinklers
installed above and around this "small" glass vestibule. This vestibule
was not the only means to exit the building, and I felt that forcing the
contractor to add one sprinkler was not money well spent. The only
cost-effective method to hide the sprinkler piping would have been to
come up from beneath the concrete floor.

Again, I think it's a case-by-case situation and not something that I
condone for all situations.
rick matsuda
city of dallas

>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
2008/7/16 RFI - Bismarck <[EMAIL PROTECTED]>:
>
>
> Forum...
>
> Have a building with a situation that I need help in addressing -
small
> entry vestibule (14'8" x 7') which has glass exterior and interior
doors and
> windows - full height; with concrete walls, floor, and ceiling
enclosing it.
> Access to this area is close to impossible...  Is there anything in
NFPA that
> I'm missing which would allow me to exclude this area?
>
>
>
> Thanks in advance.

> RFP Chuck