Undefined areas = not listed as examples in the annex A.5.2 etc... Would
moving the contents of an office into a mechanical room change the
hazard? It doesn't change the contents.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 1:35 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa
ExistingPipeScheduledSystem Water Supply)

What would be an undefined area?

I would consider a design incomplete if an area was left with no name.
Who knows what it could end up being?   

That would just be unacceptable.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, November 18, 2008 3:29 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing
PipeScheduledSystem Water Supply)

I was told a along time ago in a galaxy far away by a guy on the 13
committee (Bill Testa) that undefined areas are the same hazard as the
building they are located. Office bldg would be light hazard, mercantile
would be ordinary etc...

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Tuesday, November 18, 2008 1:21 PM
To: '[email protected]'
Subject: RE: Mech/Electrical room classification (wa Existing Pipe
ScheduledSystem Water Supply)

Oooh! Good one!

I my experience, we have done it that way out of tradition.  Maybe
because electrical/mechanical rooms can be combined; many mechanical
rooms have fuel fired equipment; both kinds of rooms often become
storage rooms (rightfully or wrongly). If some engineer doesn't specify
it, one can certainly argue in many cases that these rooms may not
warrant protection beyond light hazard. But I always spec them OH; as a
contractor we designed them that way, too.

The ND members of this forum are all too familiar with the ND Dept of
Health making them change their non-ordinary temperature heads to
ordinary because "the mechanical room is really an air handling room
with no storage and thus warrants light hazard protection and ordinary
temp heads." Never mind the additional sprinklers, additional density,
potential for future storage, and lack of human occupancy. "Those head
must be changed!"

Mark Sornsin

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, November 18, 2008 1:48 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

Out of curiosity where do come up with electrical/mechanical rooms being
OH?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

We need to be careful in our use of words here. This building is a light
hazard occupancy.

All light hazard occupancy buildings will contain some areas of Ordinary
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the
entire building, or the hose stream requirements.

While these areas must be protected per their specific hazard for
density, if your largest OH II area is only 600 Sf then you only provide
OH II density for that 600 SF area, and any smaller areas of the same
hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per
head with 5.6K will give you 0.20 at just about 7 PSI. So for your 600
Sf you would calc 8 heads unless your Light hazard area required more
than 8 heads, or was more remote, with the same number of heads.

Now because this was installed pipe schedule, you need to know if OH
pipe schedule was used in the OH areas? Actually you need to Hydraulic
the entire system to ensure the loss from the backflow will allow it to
work per NFPA 13, 2007 8.17.4.6.2.  But as far as your question goes
"The Occupancy is Light Hazard" for the use of 11.2.2.1 so 15 Psi and
the 30-60 Min.
duration
is OK.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light
in the Light Hazard Areas.  There is no "overall building design
approach"; the building is not Light Hazard unless ALL areas of the
building are light hazard.

Mark A. Sornsin, PE

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to