Thom, I think you have missed the point of my questions. And I know I don't have to calculate the entire system, all I have to do is meet the pressure/gpm demand/duration as selected from the Table. I wanted opions on which Hazard, Lower or Higher GPM's and Lower or Higher durations.
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Tuesday, November 18, 2008 12:15 PM To: [email protected] Subject: RE: Existing Pipe Scheduled System Water Supply We need to be careful in our use of words here. This building is a light hazard occupancy. All light hazard occupancy buildings will contain some areas of Ordinary hazard, such as kitchens laundry rooms, or electrical/mechanical rooms. These areas do not change the classification of the hazard for the entire building, or the hose stream requirements. While these areas must be protected per their specific hazard for density, if your largest OH II area is only 600 Sf then you only provide OH II density for that 600 SF area, and any smaller areas of the same hazard. Usually this is done by reducing the spacing per head to like 75 Sf per head with 5.6K will give you 0.20 at just about 7 PSI. So for your 600 Sf you would calc 8 heads unless your Light hazard area required more than 8 heads, or was more remote, with the same number of heads. Now because this was installed pipe schedule, you need to know if OH pipe schedule was used in the OH areas? Actually you need to Hydraulic the entire system to ensure the loss from the backflow will allow it to work per NFPA 13, 2007 8.17.4.6.2. But as far as your question goes "The Occupancy is Light Hazard" for the use of 11.2.2.1 so 15 Psi and the 30-60 Min. duration is OK. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Timothy: You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in the Light Hazard Areas. There is no "overall building design approach"; the building is not Light Hazard unless ALL areas of the building are light hazard. Mark A. Sornsin, PE _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)