How I read George's comment is that picking one piece of criteria
alone does not necessarily qualify as being that much more
conservative. Having worked at a nuke plant for a good while, there
is an extensive overall program that combined makes a very high level
of fire protection such as the referenced on-site FD as well as
trained plant personnel as well as extensive rated construction,
tightly controlled contents of rooms, enforcement of criteria, and
extensive testing and maintenance etc etc. My plant wasn't even a
reactor site but a enrichment facility where it gets really tight.
Craig: BTW, we had Lockwood Greene do some work for us. Where you
with them in the early 90's. Respond off-Forum.
Roland
On Nov 19, 2008, at 6:47 AM, <[EMAIL PROTECTED]> <[EMAIL PROTECTED]
> wrote:
You lost me there George. So through all that would you say to not
protect or to protect at a lesser degree would be adequate? Based
on......?
If you look at a mechanical room the activity going on within would
be similar to no less than OH1 (light mfg, electrical, rotating
machinery, light lubricants, minimal combustibles). I could hardly
say that it would be similar to a church or library (LH).
Electrical rooms especially if cable trays are present can pose a
greater hazard than an air handling room. Again no way to justify
LH, OH1 at minimum. Now mind you I'm not talking about residential
stuff here.
Now as far as the "when in doubt make it stout" approach, is there
any wording anywhere that states you can not increase design
criteria for an area without adopting the higher standard for the
entire facility? I haven't found that anywhere, so if I chose to
apply a criteria for a pump room that may be referenced in a Nuke
section of NFPA 13, where is it stated or implied that I have to
provide Nuke level criteria to everything else in the entire facility?
Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]
] On Behalf Of George Church
Sent: Wednesday, November 19, 2008 9:32 AM
To: [email protected]
Subject: RE: Mech/Electrical room
classification(waExistingPipeScheduledSystem Water Supply)
Craig-
I'd disagree that a specialty risk, especially when we don the nuke
mentality hat, is as readily transportable to other plain jane risks
as you state. Nuke plants revert to a higher standard of care than
the reasonable protection levels in other standards. Redundancy is a
precaution that MUST be taken- whether its derived as a requirement
in an NFPA Standard, NRC, or insurance carrier. The downside is too
great- I remember being 20 miles away from TMI and missing reading
week since our college shut down for a week. If you've seen China
Syndrome, stick Gov Thornburgh up there and you see what we lived
thru- the parallel is too scary to be coincidental.
I would agree that if you were to transport the protection
requirements for a portion of a nuke plant to a lesser risk (which
is 99.99% of anything we
see) you'd have it covered EXCEPT the caveat that it should be
understood that these requirements assume other nuke protection
levels are in place in what could be related criteria, which might
not be the case in the lesser risk the criteria are transferred to.
Let's say all nuke plants are required to have an on-site FD. Due to
this, water durations for areas "outside the fence" might be
decreased since almost instantaneous trained response is
anticipated. You shouldn't take this lessened duration and apply it
in Joey's backyard where the nearest FD could be 100 miles away.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 19, 2008 9:09 AM
To: [email protected]
Subject: RE: Mech/Electrical room classification
(waExistingPipeScheduledSystem Water Supply)
Every time there is either an electrical or fire pump room, this is
the criteria acceptable to or required by the AHJ's & Underwriters.
Regardless of whether the criteria is under the light water reactor
heading or not, if the criteria is acceptable for this type of
occupancy it is defendable for any lesser occupancy.
These rooms are the same no matter what environment they protect.
In industrial applications the fire pumps are not out on the
production floor with the hazardous material they are in a separate
building, or room same as they would be for any other occupancy so
what goes on elsewhere in the occupancy has no bearing on the
protection scheme for a pump or electrical room. If the building
requires sprinklers then the above criteria is applied.
Gas fired boilers are looked the same as a gas fired water heater,
oil fired equipment is looked at differently. Sorry but I can't
extrapolate the thoughts of those writing the codes and standards.
Height of room when you're speaking of storage IS relevant but it's
not relevant when you're talking about a space designed for
equipment. Two different things. Typically I don't see a lot of
rack storage going on in mechanical spaces. We're talking about
mechanical spaces. Fire codes prohibit storage of combustibles in
mechanical and electrical rooms.
Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, November 18, 2008 6:16 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (waExistingPipe
ScheduledSystem Water Supply)
Remember that 21.32 addresses only "Advanced light Water Reactor
Electric Generating plants" This would not be the across the board
design criteria for all M/E spaces. These plants have fuel oil and
lube pumps flowing hundreds of gallons per minute. Not quite the
same as a furnace room in a nursing home. Or a gas fired direct vent
boiler system in a school, to say nothing of the Electrical room in
either.
It would appear that it is the fuel and lube oil that drives the
density requirements. Interesting that Gas fired boilers are not
included. I wonder would that mean that Gas fueled Emergency
generators are not included also?
Probably goes back to look at the lube oil requirements.
Height of room always has code support, or why reduce the area for
QR in LH and OH occupancies? That alone says "Height Matters." OH I
has 8' storage height limitations, so Height matters. OH II has 12'
storage limitations again "Height Matters." Many storage application
sprinklers are listed for specific height building or storage
arrangements, again "Height Matters."
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Generator rooms are at .25 gpm/sf NFPA 13, 21.32.1.7
Fire Pump rooms the same. (next paragraph)
That would put them into the OH II category.
Most electrical rooms don't require sprinklers if they follow the
NFPA 13 and bldg. code requirements for rated construction and the
other items listed including no liquid filled transformers.
Elevator pits, well that's kind of obvious.
Mechanical rooms aren't given any options so height of room or other
"logic"
has no Code support.
Craig L. Prahl, CET
Fire Protection Specialist
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)