I've had it argued that 37 doesn't apply to fire pumps based on the wording in 
A.1.3.1.  Even though it says "ALSO SEE NFPA 20" being interpreted as saying to 
also refer to 20 for additional info.

If there's ever a question on what to apply contact the AHJ or Underwriter for 
clarification.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Wednesday, November 19, 2008 8:44 AM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing 
PipeScheduledSystem Water Supply)

Rooms housing emergengy generators and diesel fire pump rooms should be 
protected as EH1, per NFPA-37, "Internal Combustion Engines" standard.

Ray Vance - SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com
(407) 877-5563   office
(321) 436-2184   mobile

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: 2008-11-18 17:07
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing Pipe 
ScheduledSystem Water Supply)

I knew there was a SF limit but without looking it up I said 600 SF(Just too 
lazy today!). Thanks Ed! 400 Sf and my post remains unchanged.

The question is can we call Electric and mechanical rooms OH I? I'd say that 
one limit is if the ceiling is less than 9'-6" (18" clear below heads should 
not be more than 8'-0" high storage) why not? How about emergency generator or 
fire pump rooms?(NFPA 20, 5.12.1.1.2 only says fully sprinklered, no Design 
density.) Same kind of thing? For kitchens see A21.36.1, or 5.3.1.

And if you look at A5.4.1, Elevator Equipment rooms and pits should be EX I if 
you CANNOT prove the Hyd. Fluid is "Non-Combustible"

I would say that if the rest of the building is OH II then don't sweat the M/E 
rooms, just use the same coverage. But if the rest of the building is LH, then 
you may want to look at the actual conditions in the space.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to