Remember that 21.32 addresses only "Advanced light Water Reactor Electric Generating plants" This would not be the across the board design criteria for all M/E spaces. These plants have fuel oil and lube pumps flowing hundreds of gallons per minute. Not quite the same as a furnace room in a nursing home. Or a gas fired direct vent boiler system in a school, to say nothing of the Electrical room in either.
It would appear that it is the fuel and lube oil that drives the density requirements. Interesting that Gas fired boilers are not included. I wonder would that mean that Gas fueled Emergency generators are not included also? Probably goes back to look at the lube oil requirements. Height of room always has code support, or why reduce the area for QR in LH and OH occupancies? That alone says "Height Matters." OH I has 8' storage height limitations, so Height matters. OH II has 12' storage limitations again "Height Matters." Many storage application sprinklers are listed for specific height building or storage arrangements, again "Height Matters." Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Generator rooms are at .25 gpm/sf NFPA 13, 21.32.1.7 Fire Pump rooms the same. (next paragraph) That would put them into the OH II category. Most electrical rooms don't require sprinklers if they follow the NFPA 13 and bldg. code requirements for rated construction and the other items listed including no liquid filled transformers. Elevator pits, well that's kind of obvious. Mechanical rooms aren't given any options so height of room or other "logic" has no Code support. Craig L. Prahl, CET Fire Protection Specialist _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)