Every time there is either an electrical or fire pump room, this is the 
criteria acceptable to or required by the AHJ's & Underwriters.  Regardless of 
whether the criteria is under the light water reactor heading or not, if the 
criteria is acceptable for this type of occupancy it is defendable for any 
lesser occupancy.

These rooms are the same no matter what environment they protect.  In 
industrial applications the fire pumps are not out on the production floor with 
the hazardous material they are in a separate building, or room same as they 
would be for any other occupancy so what goes on elsewhere in the occupancy has 
no bearing on the protection scheme for a pump or electrical room.  If the 
building requires sprinklers then the above criteria is applied.

Gas fired boilers are looked the same as a gas fired water heater, oil fired 
equipment is looked at differently.  Sorry but I can't extrapolate the thoughts 
of those writing the codes and standards.

Height of room when you're speaking of storage IS relevant but it's not 
relevant when you're talking about a space designed for equipment.  Two 
different things.  Typically I don't see a lot of rack storage going on in 
mechanical spaces.  We're talking about mechanical spaces.  Fire codes prohibit 
storage of combustibles in mechanical and electrical rooms.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 6:16 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (waExistingPipe 
ScheduledSystem Water Supply)

Remember that 21.32 addresses only "Advanced light Water Reactor Electric 
Generating plants" This would not be the across the board design criteria for 
all M/E spaces. These plants have fuel oil and lube pumps flowing hundreds of 
gallons per minute. Not quite the same as a furnace room in a nursing home. Or 
a gas fired direct vent boiler system in a school, to say nothing of the 
Electrical room in either.

It would appear that it is the fuel and lube oil that drives the density 
requirements. Interesting that Gas fired boilers are not included. I wonder 
would that mean that Gas fueled Emergency generators are not included also?
Probably goes back to look at the lube oil requirements.

Height of room always has code support, or why reduce the area for QR in LH and 
OH occupancies? That alone says "Height Matters." OH I has 8' storage height 
limitations, so Height matters. OH II has 12' storage limitations again "Height 
Matters." Many storage application sprinklers are listed for specific height 
building or storage arrangements, again "Height Matters."


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Generator rooms are at .25 gpm/sf NFPA 13, 21.32.1.7

Fire Pump rooms the same. (next paragraph)

That would put them into the OH II category.

Most electrical rooms don't require sprinklers if they follow the NFPA 13 and 
bldg. code requirements for rated construction and the other items listed 
including no liquid filled transformers.

Elevator pits, well that's kind of obvious.

Mechanical rooms aren't given any options so height of room or other "logic"
has no Code support.



Craig L. Prahl, CET
Fire Protection Specialist

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to