You may want to talk to you contractor about a single supply for all four units fire system, or one larger dom. Supply in one unit and 3 smaller supplies in the other units. That way only one larger backflow, and you can still zone by unit if the GC wants, or at least by floor.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Thanks for your reply...I was thinking the same thing. We've got this subdivision where the previous FP contractor designed them to 13D's now our design is being questioned since we provided a four head calc resulting in larger BFP's, larger piping and a different style of sprinkler to be able to accomodate the low water pressure. The subdivision is wondering why our design is so different than the previous FP contractors.... gotta love it! The local AHJ is no help wither since they pretty much rubber stamp everything 'approved' anyway. A.P.Silva <[EMAIL PROTECTED]> wrote:> NO. The application of 13D/R does not depend on the water supply. If > 13R was required for a common supply, it would still be required for > individual supplies. > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)