Chapter 712 IBC 2006 Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Justin Reid Sent: Tuesday, April 28, 2009 9:22 AM To: [email protected] Subject: Re: Rating of the sprinkler escutcheon There is an exception in the building code that allows the penetration created by a sprinkler head (with escutcheon) through a horizontal assembly to not be fire sealed ( I believe in Chapter 7 somewhere IBC). It sounds like your sprinkler head may be a sidewall and penetrating the stair shaft wall. I would have to check and see if the same exception applies for vertical assemblies ( I think it does) and make sure that there are no other special situations concerning penetrating the exit (stair shaft wall). On Tue, Apr 28, 2009 at 8:12 AM, Bobby Gillett < [email protected]> wrote: > But truly with the sprinkler being semi-recessed the pipe is not > penetrating the wall the sprinkler and escutcheon are. If the cpvc is > considered pentrating the wall, could you not transition to steel > before the penetration? > > Bobby Gillett > Sr. Project Manager > Key Fire Protection, Inc. > (731) 424-0130 office (731) 424-9285 fax > (731) 267-4853 cell > [email protected] > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Sal > Izzo > (TECH- 103) > Sent: Tuesday, April 28, 2009 9:59 AM > To: [email protected] > Subject: RE: Rating of the sprinkler escutcheon > > I believe CPVC is considered a combustible penetration when running > through a rated assembly and therefore would require a listed firestop assembly. > Metal escutcheons provide no rating; the IBC permits only an > escutcheon to cover the annular space of a sprinkler penetration when > the pipe is noncombustible, i.e., steel, copper, conduit, etc. > > Regards, > > Salvatore Izzo, P.E. SFPE > Manager - Reliable Technical Services > > ________________________________________ > From: [email protected] > [[email protected]] On Behalf Of Bobby Gillett > [[email protected]] > Sent: Tuesday, April 28, 2009 10:56 AM > To: [email protected] > Subject: Rating of the sprinkler escutcheon > > Our situations - we have a hotel designed to 13R that requires our > cpvc piping to be run through a fire rated wall between two units with > 4.0K residential semi-recessed sidewall heads spraying into both > units. The other is the extended coverage 8.0K semi-recessed sprinkler > spraying into the stairwell (also fed by cpvc from the corridor). The > question being asked by the fire marshall - What is the fire rating of > the escutcheons? > > > > Bobby Gillett > > Sr. Project Manager > > Key Fire Protection, Inc. > > (731) 424-0130 office (731) 424-9285 fax > > (731) 267-4853 cell > > <mailto:[email protected]> > [email protected] > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%3ASprinklerforum-reques > [email protected]> (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%3ASprinklerforum-reques > [email protected]> (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: > [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%3ASprinklerforum-reques > [email protected]> (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)