Chapter 712 IBC 2006

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin Reid
Sent: Tuesday, April 28, 2009 9:22 AM
To: [email protected]
Subject: Re: Rating of the sprinkler escutcheon

There is an exception in the building code that allows the penetration
created by a sprinkler head (with escutcheon) through a horizontal assembly
to not be fire sealed ( I believe in Chapter 7 somewhere IBC). It sounds
like your sprinkler head may be a sidewall and penetrating the stair shaft
wall.  I would have to check and see if the same exception applies for
vertical assemblies ( I think it does) and make sure that there are no other
special situations concerning penetrating the exit (stair shaft wall).

On Tue, Apr 28, 2009 at 8:12 AM, Bobby Gillett <
[email protected]> wrote:

> But truly with the sprinkler being semi-recessed the pipe is not 
> penetrating the wall the sprinkler and escutcheon are. If the cpvc is 
> considered pentrating the wall, could you not transition to steel 
> before the penetration?
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Sal 
> Izzo
> (TECH- 103)
> Sent: Tuesday, April 28, 2009 9:59 AM
> To: [email protected]
> Subject: RE: Rating of the sprinkler escutcheon
>
> I believe CPVC is considered a combustible penetration when running 
> through a rated assembly and therefore would require a listed firestop
assembly.
> Metal escutcheons provide no rating; the IBC permits only an 
> escutcheon to cover the annular space of a sprinkler penetration when 
> the pipe is noncombustible, i.e., steel, copper, conduit, etc.
>
> Regards,
>
> Salvatore Izzo, P.E. SFPE
> Manager - Reliable Technical Services
>
> ________________________________________
> From: [email protected]
> [[email protected]] On Behalf Of Bobby Gillett 
> [[email protected]]
> Sent: Tuesday, April 28, 2009 10:56 AM
> To: [email protected]
> Subject: Rating of the sprinkler escutcheon
>
> Our situations - we have a hotel designed to 13R that requires our 
> cpvc piping to be run through a fire rated wall between two units with 
> 4.0K residential semi-recessed sidewall heads spraying into both 
> units. The other is the extended coverage 8.0K semi-recessed sprinkler 
> spraying into the stairwell (also fed by cpvc from the corridor). The 
> question being asked by the fire marshall - What is the fire rating of 
> the escutcheons?
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>  <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to