If this is a framed wall with the piping entirely within the wall and only the 
sprinkler is penetrating one membrane (the Type X GWB) you really are not 
penetrating a fire barrier.  This is similar to an electrical receptacle that 
openetrates one membrane in a framed wall, which is explicitly permitted by the 
NEC.  This would be different if you ran a CPVC pipe into a rated elevator 
shaft or stair shaft that went entirely through the wall.  In that case, you 
would typically need to provide the UL-listed, intumescent sleeve fire-stopping 
system.

I recall the NFSA rep at the ICC hearings addressing this issue and it was 
clarified in Chapter 7 of the IBC.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 


--- On Tue, 4/28/09, [email protected] <[email protected]> wrote:

From: [email protected] <[email protected]>
Subject: RE: Rating of the sprinkler escutcheon
To: [email protected]
Date: Tuesday, April 28, 2009, 10:33 AM

And is that assuming that the pipe penetrating the membrane is of noncombustible
materials? 

Any time you breach rated construction either the material penetrating has to
be non-combustible or you provide a UL Listed , non-combustible sleeve assembly
that is sealed at both ends.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson, Duane
(NIH/OD/ORS) [C]
Sent: Tuesday, April 28, 2009 11:28 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

IBC 712.3.2 #3 provides an exception to penetration protection of 1-hr partion:
 The annular space created by the penetration of a fire sprinkler provided it is
covered by a metal escutcheon plate.


Duane Johnson, PE

Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services
National Institutes of Health
301-496-0487

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, April 28, 2009 11:07 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

Not measurable.  If the wall is to be 1hr rated construction, the fire stopping
material for the penetration must provide equal.  How would you measure the
value of the sprinkler in relation to hours of equivalent resistance?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, April 28, 2009 11:03 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

What about the sprinkler itself? Doesn't it offer something of value at the
point of penetration?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sal Izzo (TECH-
103)
Sent: Tuesday, April 28, 2009 9:59 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

I believe CPVC is considered a combustible penetration when running through a
rated assembly and therefore would require a listed firestop assembly.  Metal
escutcheons provide no rating; the IBC permits only an escutcheon to cover the
annular space of a sprinkler penetration when the pipe is noncombustible, i.e.,
steel, copper, conduit, etc.

Regards,

Salvatore Izzo, P.E. SFPE
Manager - Reliable Technical Services

________________________________________
From: [email protected]
[[email protected]] On Behalf Of Bobby Gillett
[[email protected]]
Sent: Tuesday, April 28, 2009 10:56 AM
To: [email protected]
Subject: Rating of the sprinkler escutcheon

Our situations - we have a hotel designed to 13R that requires our cpvc piping
to be run through a fire rated wall between two units with 4.0K residential
semi-recessed sidewall heads spraying into both units. The other is the extended
coverage 8.0K semi-recessed sprinkler spraying into the stairwell (also fed by
cpvc from the corridor). The question being asked by the fire marshall - What is
the fire rating of the escutcheons?



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to