Out here in CT (and central MA), it varies all over the lot. Typically if I hear anything it is 1 year. To some extent, it also depends on the location. Some areas go longer because it is difficult to get a flow test. Of course, in other areas, you could submit a flow test from the 1870s and it would be accepted, provided there was a PE stamp on the drawing. But 1 year is pretty typical.
At 01:02 PM 5/12/2009, you wrote: >We are reviewing our policy as to the length of time for use of >hydrant flow test data. > >We have heard ranges from as short as 6 months to 18 months. > >If the forum members would be willing to share thoughts as to how >old of a test is accepted by the AHJ's you deal with it can help >guide our revised policy. > >Thanks in advance, > >Rich Richardson >Seattle Fire Department > > > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)