I think the statistic is 1:16m heads leak. Could be 13m. So yes, It's
possible and has occurred often enough that there is a statistic.
Usual culprit is fitters banging heads around in a  bucket and the
result might not show up for years.

On Tue, Dec 1, 2009 at 8:54 AM,  <[email protected]> wrote:
> Exactly. Bulb is intact. No chance of freezing. No chance of being hit.  With 
> the rust it's been going on a while.  Fitter didn't look at other heads.  
> We've not seen this much.  Thought it was related to Central and o-rings 
> only.  Has anyone else had experience with non-o-ring and non-Central heads 
> weeping and rusting?  These are 25 yo Viking.
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: "Thom McMahon" <[email protected]>
> Date: Tue, 1 Dec 2009 09:13:02
> To: <[email protected]>
> Subject: RE: O-rings/leaking seat
>
> Just a comment, and I haven't been following this thread that closely, but
> didn't you say green "Rust", which would indicate corrosion of the brass
> seat to me. Just a thought.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of David de
> Vries
> Sent: Monday, November 30, 2009 8:30 PM
> To: [email protected]
> Subject: Re: O-rings/leaking seat
>
> Chris:
>
> I believe Ron is right that Viking never made sprinklers with O-ring seals
> in the waterway.  When they started making glass bulb, QR sprinklers, they
> went with the Belleville spring seal, which was the type of seal that
> replaced the O-ring seal in the Central sprinklers.  The oldest of their 8
> mm bulb sprinklers that I have on my desk  is 1988 and it also has the BV
> seal.
>
> Could your sprinkler have been exposed to freezing temps?  I have seen
> sprinklers with BV seals that were frozen, the seal displaced, and then
> dribbled when the thaw happened.  The seal is a thin piece of Mylar (or
> generic equivalent, I believe) and it bulges out away from the spring.
>
> There are other mfrs that made O-ring sealed waterways.  Go to UL's website
> and look around, or contact me off forum.  To my knowledge only Central and
> a limited number of Gem and Star sprinklers were recalled due to O-ring
> problems.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
>
>
> --- On Mon, 11/30/09, Chris Cahill <[email protected]> wrote:
>
>
> From: Chris Cahill <[email protected]>
> Subject: O-rings/leaking seat
> To: [email protected]
> Date: Monday, November 30, 2009, 11:20 AM
>
>
> We've only been following the issue a little bit.  I know about the recall
> on Central heads so that's not the question.  The question is - are there
> other brands that are "rusting" and leaking from the seat?  I've got a
> Viking head from 1984 (might be a model XHH) that was leaking.  It has a
> flat cap much like the Central o-ring heads.  It has a green "rust" line
> around the seat.  Is there other brands with o-ring, were they subject to
> recall?  Is the leaking caused by an o-ring, maybe I'm mixing two different
> issues?
>
>
>
> Chris Cahill, P.E.
>
> Fire Protection Engineer
>
> Sentry Fire Protection, Inc.
>
>
>
> 763-658-4483
>
> 763-658-4921 fax
>
>
>
> Email: [email protected]
>
>
>
> Mail: P.O. Box 69
>
>         Waverly, MN 55390
>
>
>
> Location: 4439 Hwy 12 SW
>
>               Waverly, MN 55390
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________