Chris:
 
I believe Ron is right that Viking never made sprinklers with O-ring seals in 
the waterway.  When they started making glass bulb, QR sprinklers, they went 
with the Belleville spring seal, which was the type of seal that replaced the 
O-ring seal in the Central sprinklers.  The oldest of their 8 mm bulb 
sprinklers that I have on my desk  is 1988 and it also has the BV seal.
 
Could your sprinkler have been exposed to freezing temps?  I have seen 
sprinklers with BV seals that were frozen, the seal displaced, and then 
dribbled when the thaw happened.  The seal is a thin piece of Mylar (or generic 
equivalent, I believe) and it bulges out away from the spring.
 
There are other mfrs that made O-ring sealed waterways.  Go to UL's website and 
look around, or contact me off forum.  To my knowledge only Central and a 
limited number of Gem and Star sprinklers were recalled due to O-ring problems.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Mon, 11/30/09, Chris Cahill <[email protected]> wrote:


From: Chris Cahill <[email protected]>
Subject: O-rings/leaking seat
To: [email protected]
Date: Monday, November 30, 2009, 11:20 AM


We've only been following the issue a little bit.  I know about the recall
on Central heads so that's not the question.  The question is - are there
other brands that are "rusting" and leaking from the seat?  I've got a
Viking head from 1984 (might be a model XHH) that was leaking.  It has a
flat cap much like the Central o-ring heads.  It has a green "rust" line
around the seat.  Is there other brands with o-ring, were they subject to
recall?  Is the leaking caused by an o-ring, maybe I'm mixing two different
issues?



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [email protected]



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to