100 lbs... not 100 gallons.

If your system requires 35 gpm and you do a bucket test for 30 
seconds, in theory, you will get at least 17.5 gallons of water. At 
8.35 lbs/gallon, that is approximately 146 lbs of water on carpeted, 
painted and furnished space you will need to remove without spilling 
a drop, lest you call out the mold police.


At 03:00 PM 12/21/2009, you wrote:
>You know you CAN produce a suction line by sucking really hard- the local
>inspector should have plenty of zip....
>
>And to get 100 gallons in there in a minute from a K4.4 head, boy you must
>have tanks atop some really big hills. Like a tank 1,000' uphill, since
>you'd need about 500 PSI to get 100 GPM out of a K4.4. Might want to run the
>test at only 30 seconds, and I'd check that end head restraint, cover the
>trash can for the inevitable splash.
>
>So do you hydro at 550?
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of G. Tim Stone
>Sent: Monday, December 21, 2009 2:48 PM
>To: [email protected]
>Subject: RE: Bucket test
>
>Todd,
>
>Pump it off into the nearest toilet or window would be my suggestion.
>
>G. Tim Stone
>
>
>NICET Level III Engineering Technician
>Fire Protection Sprinkler Design
>and Consulting Services
>
>117 Old Stage Rd. - Essex Jct., VT. 05452
>TEL: (802) 434-2968          Fax: (802) 434-4343
>                 [email protected]
>
>
> > -----Original Message-----
> > From: [email protected] [mailto:sprinklerforum-
> > [email protected]] On Behalf Of Todd Williams
> > Sent: Monday, December 21, 2009 2:43 PM
> > To: [email protected]
> > Subject: Re: Bucket test
> >
> > Thanks. One question: How do you get a trash can with 100# of water
> > off the third floor of a house without creating a disaster?
> >
> >
> > At 02:11 PM 12/21/2009, you wrote:
> > >Todd,
> > >Take a 1" copper or CPVC pipe, 5' long. On one end place male
> > >threads to be screwed into the over head. At the other end place a
> > >female connection for the sprinkler head (break the deflector off).
> > >In between place a 1/4 turn valve. Place a 30 gal trash can
> > >(pre-marked at gallon increments) under the pipe. Charge the system,
> > >bleed the air, open the valve and time it for one minute.  There ya
> > go!
> > >Hope that helps.
> > >Owen Evans
> > >Redondo Beach Fire Dept.
> > >
> > > >>> Todd Williams <[email protected]> 12/21/2009 10:23 AM >>>
> > >Does anyone have a good description of how to do a bucket test? I
> > >have a client who has been asked to do one on a 13D system but hasn't
> > >done one before. I have a general idea, but would appreciate input
> > >from someone with more experience.
> > >
> > >Todd G. Williams, PE
> > >Fire Protection Design/Consulting
> > >Stonington, Connecticut
> > >www.fpdc.com
> > >860.535.2080
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > >(Put the word unsubscribe in the subject field)
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > >(Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > (Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to