I agree with Todd that you would be better off if someone else made the call.  
Or are you bidding a design/build project?  Perhaps share the load by hiring an 
engr as a sub to you.
 
Other thoughts:
 
How about the owner's certificate -- now required by 13?  Can you get a 
commitment on product and quantity from Ace?
 
If you are going to try and figure this out on your own, look at the volume of 
polystyrene foam as a percentage of product volume.  IFC has both weight and 
volume percent limitations to call it Class IV.  There is also a limit on how 
much Group A you can have without classifying the whole place as Group A.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Mon, 12/21/09, Todd Williams <[email protected]> wrote:


From: Todd Williams <[email protected]>
Subject: RE: Ace hardware classification
To: [email protected]
Date: Monday, December 21, 2009, 1:33 PM


I wouldn't make a commodity class call without looking at the actual 
product. In a perfect world, they should have a PE or at least the 
insurance carrier making that determination. Does ACE have a standard 
specification?



At 02:03 PM 12/21/2009, you wrote:
>We've been looking at an ACE brand hardware/home center store, and trying to
>decide if it's class III or class IV commodities. They've already screwed up
>any possible OH II (Mercantile) because they have single row shelves and
>single row solid shelve racks with the top shelve or solid shelve rack at
>12'-0" AFF (So storage to 16'-0") around the perimeter of the store. (About
>360LF of rack or shelves) What we see in other ACE stores is this top shelve
>is used to store excess inventory. Most of it in boxes with polystyrene foam
>holding the product in place. I say this is class IV with the allowed
>plastics.
>
>Any input?  III or IV?
>
>As a secondary issue is the paint area. Per NFPA 30 10.7.1 OH II with
>increased design area? (Top shelve is 84" of Back to Back shelves) What
>always scares me about these areas is the close proximity of the Aerosol
>cans and oxidizers (Deck cleaners)to the flammable and combustible liquids.
>
>Any thoughts?
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to