Couple of thoughts: 24 is mostly augmentation to the typical underground installation standards applicable when the UG is private fire service main. 24 does not apply to public installation but can.
We get hung up on listings because we use them all the time. Other trades don't. Isn't pipe and fittings traditionally used in sprinkler work exempt from requiring a listing per 13? Galvanized pipe can be directly buried. Ductile can be directly buried. Grooved couplings and fittings are ductile. Gas pipe has to be black steel which cannot be directly buried so buried gas line has to be coated to X mils (I forget exactly) and the joints and fittings also. Presumably black ductile threaded fittings on gas line would not need coating. On Thu, Mar 25, 2010 at 2:22 PM, Thom McMahon <[email protected]> wrote: > Good luck with that! It's like trying to find a listing for ductile Iron > Pipe above ground for fire protection. The most often listed reason not to > use PVC (C900) above ground is it's not listed. Well try and find a DIP > that's listed for Fire Above ground. > > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: 970-879-7952 > Fax: 970-879-7926 > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of George Church > Sent: Thursday, March 25, 2010 3:28 PM > To: [email protected] > Subject: RE: Grooved Underground, Thrust Blocks Required? > > I'd check vic and/or Grinnell websites/manuals. > > I've run grooved galv, wrapped, to a 90* pattern FDC without serious > consequences. > > glc > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)