"Isn't pipe and fittings traditionally used in sprinkler work exempt
from requiring a listing per 13?"

As long as it meets one of the standards listed in NFPA 13.

Personnaly, I would not think that a listing is required for a coupling
or fitting to be used in the underground.  It is listed for fire
protection use.  We use them all the time with a galvanized coating, tar
and wrap and never had a issue.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES


-----Original Message-----
From: [email protected]
[mailto:[email protected]
<mailto:[email protected]> ] On Behalf Of Ron
Greenman
Sent: Thursday, March 25, 2010 8:59 PM
To: [email protected]
Subject: Re: Grooved Underground, Thrust Blocks Required?

Couple of thoughts:

24 is mostly augmentation to the typical underground installation
standards applicable when the UG is private fire service main. 24 does
not apply to public installation but can.

We get hung up on listings because we use them all the time. Other
trades don't. Isn't pipe and fittings traditionally used in sprinkler
work exempt from requiring a listing per 13?

Galvanized pipe can be directly buried. Ductile can be directly buried.
Grooved couplings and fittings are ductile. Gas pipe has to be black
steel which cannot be directly buried so buried gas line has to be
coated to X mils (I forget exactly) and the joints and fittings also.
Presumably black ductile threaded fittings on gas line would not need
coating.


On Thu, Mar 25, 2010 at 2:22 PM, Thom McMahon <[email protected]>
wrote:
> Good luck with that! It's like trying to find a listing for ductile
> Iron Pipe above ground for fire protection. The most often listed
> reason not to use PVC (C900) above ground is it's not listed. Well try
> and find a DIP that's listed for Fire Above ground.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]
<mailto:[email protected]> ] On Behalf Of George
> Church
> Sent: Thursday, March 25, 2010 3:28 PM
> To: [email protected]
> Subject: RE: Grooved Underground, Thrust Blocks Required?
>
> I'd check vic and/or Grinnell websites/manuals.
>
> I've run grooved galv, wrapped, to a 90* pattern FDC without serious
> consequences.
>
> glc
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to