Without going into another code, is the occupancy a residential occupancy?
Does your community development plan allow for office in single family
homes? 

If you're not changing from and R to a B classification what is your
question. How many new homes don't have home office's? Just because this one
adds a waiting room, doesn't really increase the risk or occupancy. I can't
see a shrink with 3 or four nurses, a receptionist and 10 or 12 patients
backed up. Heck we just did a group home for "Challenged" clients with 13D
as required by NFPA 101. You may have one or two 'challenged people there at
one time but certainly not 10.

So two head 13D is ok in my opinion.


Now onto the Codes. IRC 419.5 

419.5 Fire Protection: the live/work unit shall be provided with a monitored
fire alarm system where required by Section 907.2.9 and an automatic
sprinkler system in accordance with Section 903.2.8

903.2.8 Group R.  An automatic sprinkler system installed in accordance with
Section 903.3 shall be provided throughout all buildings with Group R fire
area. 
(903.3 allows 13D)
903.3 Installation requirements. Automatic sprinkler systems
shall be designed and installed in accordance with Sections
903.3.1 through 903.3.7.
903.3.1.3 NFPA 13D sprinkler systems. Where
allowed, automatic sprinkler systems installed in one and
two-family dwellings shall be installed throughout
in accordance with NFPA 13D.


907.2.9 Group R-2. Fire alarm and smoke alarms shall be installed in Group
R-2 occupancies as required in Sections 907.2.9.1 and 907.9.2 

907.2.9.1 Manual Fire Alarm System



Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, March 25, 2010 6:19 PM
To: [email protected]
Subject: Re: 13D Question

Tom,

I was just at an SFPE seminar in Norwood that went over changes for 
the 8th edition of the MA Code. There is a new section 419 that 
addresses Live/Work situations, to which this would apply. Try going 
on to the web site and see what they call for.

Todd


At 08:00 PM 3/25/2010, you wrote:
>Got a SFD 13D system I designed and almost ready for installation.
>The Owner, a psyche has decided to move his practice home and make the
>Basement his Office.
>I'm a little concerned about the big open waiting area he wants to make, 5
>heads to cover.
>It was all cut up before, no more than 2 heads per room, finished.
>It's clearly out of 13D criteria and I can't support even 4 heads, I tried,
>even with minimum spacing.  Plus, the service is already in so I can't ask
>to have it increased.  I did tell him tamper switches were required and
some
>real sort of fire alarm (we were just putting in a bell and interconnecting
>the smokes plus his security system to the flow switch).  I've told him we
>have a problem so he wants to do it later.
>
>I need to write him a letter to posture and protect myself because we're
>going forward with the family room, in-law bedroom and toilet, and storage
>rooms as drawn.  Anybody done this?
>
>Thanks Campers!
>
>Tom
>Go Red Sox!!
>(opening night with the spankees and no beer served at fenway)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to