It's still a single family dwelling why are YOU upgrading the occupancy?
Thomas Poisal, CET

On Thu, Mar 25, 2010 at 8:00 PM, Tom Duross <[email protected]> wrote:

> Got a SFD 13D system I designed and almost ready for installation.
> The Owner, a psyche has decided to move his practice home and make the
> Basement his Office.
> I'm a little concerned about the big open waiting area he wants to make, 5
> heads to cover.
> It was all cut up before, no more than 2 heads per room, finished.
> It's clearly out of 13D criteria and I can't support even 4 heads, I tried,
> even with minimum spacing.  Plus, the service is already in so I can't ask
> to have it increased.  I did tell him tamper switches were required and
> some
> real sort of fire alarm (we were just putting in a bell and interconnecting
> the smokes plus his security system to the flow switch).  I've told him we
> have a problem so he wants to do it later.
>
> I need to write him a letter to posture and protect myself because we're
> going forward with the family room, in-law bedroom and toilet, and storage
> rooms as drawn.  Anybody done this?
>
> Thanks Campers!
>
> Tom
> Go Red Sox!!
> (opening night with the spankees and no beer served at fenway)
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to